Answer / alpglk
Typical Operating times for HV/EHV/UHV Circuit Breakers
Tripping/Opening: 25-40ms
Closing: 80-140ms
| Is This Answer Correct ? | 10 Yes | 1 No |
Answer / sreekanth bammidi
Generally the operating time of the circuit breakers
depends on the designer. The opening time of the breaker
should be less than the closing of the breaker. Opening
time should be less than or equal to 20msec (preferrable).
Closing time depends but preferrably less than 90msec.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / arun
Circuit breaker closing tome 60 msec
triping time lessthan 40msec
| Is This Answer Correct ? | 8 Yes | 9 No |
Answer / vijay mali
Generally the operating time of the circuit breakers
depends on the designer. The opening time of the breaker
should be less than the closing of the breaker. Opening
time should be less than or equal to 20msec (preferrable).
Closing time depends but preferrably less than 90msec
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / rajesh kumar
circuit breaker closing time 40msec.
circuit breaker tripping time less than 20 msec.
| Is This Answer Correct ? | 4 Yes | 8 No |
how we calculate the motor rating of pump for water suction ?its any formula for that plz give thank u
What will the effect on a motor designed at 60 HZ, and operated on 50 HZ ??
Whats parameters which we keep in mind when grounded any electrical machine.
in transmission line 11kv is step up or step down? why?
what is the control circuit for operating the clean room air shower
what is the main function of lbb protection
working principle of AC Servo Motor with its construction
Can we provide 3phase wire in conduit for room?
type of transformer
Double Busbar Scheme for outdoor switch yard system (132kv) step up power plant Hi friends 1. in this system both busbars energized all the time. 2. what is the meaning of main BB and transfer BB, 3. step up transformer connect main bus bar all the time or both BB connected through DS switch . 4.bus sectionalization means ? thank you.
is that a problem if i connect a single phase load to a secondry delta connected transformer but i get a neutral from other transformer i the system?
what happens if we connect two parallel ideal voltage sources across resistor?what is current flowing through resistor?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)