Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...

what is the breakdown voltage value in BDV test in
transformers?

Answer Posted / nitin arora

It depends on the voltage rating of the transformer
IF transformer rating is less than 72 KV then minimum BDV should be 30 KV.
IF transformer rating is 72 to 170 KV then minimum BDV should be 40 KV.
IF transformer rating is more than 170 KV then minimum BDV should be 50 KV.

All above results are referring the 2.5 MM gap during test.

Is This Answer Correct ?    6 Yes 0 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

how to calculate percentage impedence at 75 deg C at normal tap

2206


Anyone who can recommend an equivalent to Envirotemp FR3 of Cooper?

1915


What is the gross weight to copper ratio in slip ring induction motor of 4000 HP,6.6 kv, 372amp, 992 rpm GE motor.

2300


For an induction motor wat is the loading/unloading cycle duration or interms of L/UL ratio/ percentage?

2015


At what factor resistance r of a conductor depends?

1057


can u give me a brief idea about power line carrier communication ??

1915


Can 33kva/415v transformer be run underground? If the answer is yes why and if the answer is no why?

1519


Whether amorphous core transformer is available in India?.If available then up to what rating of voltage and KVA?.

1677


what are the main applications of transistor in non-linear region?

1969


2. What are the parameters of EHT sub-station?

2304


what is circuit recombiner and how it is different from circuit breaker

1805


please write motor, transformer, Generator setting, fault level calculation of Tr.etc

2008


hi, i have 3x200KVA and 2 x 80KVA UPS with battery bank of 150AH 68Nos. and 100AH 204Nos., i need to install AC either ductable or PAC type, so can you help me to calculate heat load and capacity of the AC to install.

2681


why ct's&pt'S out put called as burden,why compelsary short ckt the secondary of ct's while removing the burden?

2159


how generator avr give to the input?

1937