We have a 33/11kv switchyard having 12.5 MVA power
transformer. We export & import power through this
transformer. When we export power, the PF will be depend on
GRID PF & when we import power the PF will be depend on our
load PF. but the problem is that,when neither we export nor
import but our 33KV vCB is in close position,our meter read
the power factor 0.14 to 0.25 at that moment. So how can be
we improve the power factor at that moment.
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
You should realise that when there is no load on
transformer, the pf is almost zero
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / vinova
try to put some light load on your transformer during this
period if you you wnt to keep the pf high during this
period. it happens because under no load condition the
power fector angle is near 75 and power fector is high. it
happens because tansformer need reactive power for
energising its magnatic circuit. as the outer load is zero
during no load the internal load of transformer is
inductive.
| Is This Answer Correct ? | 2 Yes | 1 No |
are load variation in your plant? If variation for some minutes are in your plant then this problem should be created. In load time power factor was normal but on no load time power factor was abnormal, because we have maintain the power factor in on load position.At no load time capacitive power has make a leading power factor.for detail pl. cont. to Ab. Khalil 9977278622
| Is This Answer Correct ? | 1 Yes | 0 No |
What are the advantages of star-delta starter with induction motor?
7 Answers Merchant Navy, Naval Academy, Samundra Institute of Maritime Studies, YMCA,
I have 4 DG set with 1500KVA rating. system breakers are 11KV & alternator are 415 Volts. i want to Know what is max. resistance for body earthing & 415 & 11KV V Neuteal earthing. my fault current is 14 times for 2 sec.
What is the difference between type1 and type2 relay protection co-ordination for motor feeders
What should be the percentage increase in length of the dead end clamp for bus bar conductor (Hawthorn) after hydraulic pressing and what should be the applied pressure?
how the harmonics are generated in transforemer?
i installed 100kva ups. what KVA genset they should provid in input side? plz any update formula or ans with reason.
What is the difference between synchronous motor & asynchronous motor
if single phase is having 220v supply then why three phase is having 440v instead of 660v?
What is online and offline ups? how does it works?
How to arrange a hous hold earthing system to keep minimum earth resistance( below 7ohms).
What is the difference between rulling span and wind span of of an Over Head Transmission Line?
how to avoid electrical shock how capacitor store charges wat are the speed control of induction motors state faradays law flemings left hand rule what is rotary converter wat is transmission and distribution what are the sources of energy abrevation of acb,vcb,sf6,igbt what is output equation of transformer which test copper iron and iron loss are calculated what is eddy current draw a single line diagram (10 marks) draw direct online starter(10 marks)
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)