How to calculate CT ratio for 11KV 1500KVA Transformer
500KVA MD and 1400KVA connected load ?
Note:- As per MSEB(Maharastra state electricity Board)
Answer / k.prakashchandra
Max current based on Tr capacity is 79A. hence rated primary
current of ct would be 100A.If development is not expected 75 A
Is This Answer Correct ? | 5 Yes | 3 No |