How to calculate CT ratio for 11KV 1500KVA Transformer
500KVA MD and 1400KVA connected load ?
Note:- As per MSEB(Maharastra state electricity Board)
Answer / k.prakashchandra
Max current based on Tr capacity is 79A. hence rated primary
current of ct would be 100A.If development is not expected 75 A
| Is This Answer Correct ? | 5 Yes | 3 No |
How to calculate cable size? How to O&m of vcb?
What are the drawbacks of HVDC system?
What is the actual formula for transformer short circuit test? below i given rating of the transformer.. 1000KVA, pri 11KV, Pri amp 56A. %Z 5.95..
Technical equations
How do you calculate of power factor, if it is lagging or leading for unit(1).
we convert 66kv to 33 kv to 11kv to 440v. why can't we directly convert 33kv to 440 ?
25 kva load,
one split ac how can told of this ac which Tr tell me us
What if the difference beween internal and exrteranal LBB?
How would you relate your key competencies to this position?
how to calculate the input current in singel phase and 3phase supply to 5kva ups
In cable sizing calculation (determining the max route length of cable) why we choose the shortest length between cable length of full load current Iflc & starting current Istart?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)