why 30 ma elcb is used ?why cant 100 ma?
Answers were Sorted based on User's Feedback
Answer / hardik vyas
30 mA ELCB is used for human protection. Cause the current
which is passing through human body, exeeds 15 mA then it
can cause serious injury or even fatality. Here if your
ELCB is 30 mA, it will trip before it reaches 15mA...
Is This Answer Correct ? | 47 Yes | 15 No |
Answer / francis
elcb is speacially used to prevent earth leakage. The 30ma
is the value of current which a system can handle boyound
this it will affected the system even a human body also
Is This Answer Correct ? | 14 Yes | 8 No |
Answer / satyabrata mahapatra
If we put 40 amps ELCB it can't trip within a shorter
momment & rate of flow of current increase beyond the human
body resistance capacity.
Is This Answer Correct ? | 4 Yes | 6 No |
derive the e.m.f equation of transformer
Why we oil in tranformer/
suppose we using 3 phase motor of 440 v means what range of C.T. is require for measuring current , the rating of motor is 1HP ?
what happens when a power transformer neutral earthing broken???
what is bus coupler, where it used.
What is reason to get a power factor nearly zero in resistive loads
URGENT PLEASE//////////A WORK SHOP IS HAVING A 100 KVA TRANSFORMER 11KV/415 VOLTS, AND THE CONNECTED LOAD OF THE WORK SHOP IS 80 KW WITH INDUCTIVE LOADS, LIGHTING LOADS,ETC., HOW MANY EARTH ELECTRODES ARE NEEDED AND WHAT IS THE EARTH RESISTANCE OF EACH EARTH ELECTRODE AND COMBINED EARTH RESISTANCE in normal soil. AT 11 KV SIDE AND AT LT SIDE. HOW TO CALCULATE.
What is meant by inverse definite mean time (IDMT)& definitemean time (DMT)?
what is AVP?
What are the section criteria for cables. Now everywhere XLPE power cable is used or PVC is also used?.
what do you mean by puncturing of insulator by ice -coating?
Can i use to 3 phase 4 wire energy meter inplace of 3 phase 3 wire energy meter ?