what is the best way to start a 15 KW motor for pump star-delta or direct on line ?
and from how many KW i must use direct on line ?
15kW motor is small load categorized, DOL will be the best choise, you need at least 6 to 8 times of kW at motor starting
Is This Answer Correct ? | 1 Yes | 1 No |
how to use single phase supply for a three phase equipement.
does the power factor of an induction motor improve upon used in parallel with a synchronous condenser , used commonly to provide a leading kva ?
highest rating of alternator used in india
what sq.mm copper pvc wire need for ac load current 25amps for 230v ?
A circuit breaker on detecting fault will a. Open b. Close c. Open and trigger the alarm
'documenˁ
Lux meter is the measuring device to measure the lux level of lighting fixture. in industrial sector two types of lighting fixture is being used as street lighting purpose 1. HPSV (Sodium) and 2. HPMV (Mercury). HPMV having white light which is an combination of red, blue and yellow colour, while HPSV haivng Yellow lighting. in HPSV red & blue colour will be absent. during measurement of the lux level of HPSV and HPMV fixture. 1. Lux meter can measure the actual lux level of both fixture? 2. or it will show false reading for HPSV fixture light as it has only yellow light present. please give me answer
how power saving takes place through VFD?
what happens if you swap F1 and F2 connection in the exiter of the generator?
if the back emf eqution for dc motor EB=(QPNZ/60A) THEN what is the value of A for PMDC MOTOR OR how can dicide the value of "A"
which motor will u use in refinaries?
A 150KW 440V motor is need to replace in the field instead of faulty one. what are the main parameter should I need to check?