What is basic fundamental for choosing NGR or NGT for any
generator neutral grounding
Answer Posted / vishal i vadodaria
As we know that in Y connection there are 3 phases [R,Y&B] & a neutral.
In neutral we provide a resistance & than we used to ground it.Such system called neutral ground resistance [NGR].
Why we use NGR?
AS we know ideally the sum of current Ir+Iy+Ib is zero. So in normal condition the current which flow through neutral of Y winding is very low.
In case of occurrence of phase to phase or phase to ground fault heavy unbalance current will be generated & that will flow through neutral. To restrict this current we provide a resistance in neutral.
If we do not provide resistance in neutral & fault occurs at that time a heavy current will flow & it cause excessive heating in stator winding & it may damage the winding. to prevent this we provided a resistance in neutral.
| Is This Answer Correct ? | 60 Yes | 9 No |
Post New Answer View All Answers
Dear sir, How to calculate 3.5 core pvc aluminium armoured cable meter wise carrying amps rating.Please give the solution with a good example.
Why single phase induction motors are not self starting ?
The ripple frequency in output of fullwave bridge rectifier is a. Half the input b. Twice the input c. Same as input
Why the efficiency of generator is more than motor in swinburne's test
what is difference between isolation and ultra isolation transformer?, what is the method of testing ?
what is the relationship between phase & neutral
What are the various types of BUSBAR Schemes? explain each
am commissioning the trafo without connecting the neutral therefore unbalance will occur what is the alternative solution for this?
defult setting in p220 micom motor proction relay for 11kv,640kw,f.l.a.-40a,1440rpm ht motor?
What is the vector group of a transformer,how can it be found out?
How cmd is calculated in case of energy neters
Why the efficiency of a three-phase induction is the motor is less than that of a three-phase transformer?
what is difference between earthingpits,earthing grid & earthing mess?
What are the three constants associated with a steady state error?
What are the advantages of speed control using thyristor?