1-What is the difference between absorption factor and
polarization factor in insulation resistance test in
transformers?
and why we inject until ten minutes to get
polarization factor?
Answer / m.waqas(electrical)
both of the techniques are the same .
IN polarization index method the molecules of water are polarized and it takes almost ten mints to polarize the water molecule by using megger. This test is performed in field or you can say on used transformer or on that transformer which remain idle (not in use for long time with oil present in it) where there is a chance of moister presence due to condensation.
The dielectric absorption technique is used for type test(test perform after making transformer) here transformer is new and moister is just remove. As we all know absorption method is quicker than that of polarization(ratio of resistance measured 15 sec to 1 minit ).
BUT polarization technique is always preferred for good results or reliable results.
| Is This Answer Correct ? | 1 Yes | 0 No |
How we can make sure cable size of LT cable without any parameter.
2 Answers Paradip Port, Siemens,
How do i perform grounding of star point of Genset (400V) for making connection with step up transformer of DELTA-DELTA (400V to 20KV) ? while Genset itself has its own neutral and grounding bus bar inside genset breaker box whereas we have another neutral and grounding busbar in synchronizing panel next to genset at maximum distance of 6meter, would someone pls advice if we can only perform neutral grounding in synchronizing panel or should we ground neutral on both places inside genset breaker box and synchronizing panel.
for same rating of a transformer and induction motor which one will have higher magnetising current flowing?
why is the transmission voltage is multiple of 11?
WHAT ARE THE SITE TEST APPLIED ON A SURGE ARRESTORS? DO MEGGER TEST APPLIED ON SURGE ARRESTOR? IF YES THEN WHAT ARE THE ACCEPTED IR VALUE REQUIRED FOR SURGE ARRESTORS FOR VOLTAGE LEVEL 11KV, 33KV, 66KV 132KV, 220KV AND 400KV?
difference between microprocesser and microcontroler
What are the Safety measures in central chiller plant? Explain them?
22 Answers Carrier, CPIC, HSL, JLL,
When we getting shock, its we getting from voltage or Current.
If a capacitor bank is having rating 750kvar for 6.6kv. Then for 3.3kv how much will be the rating of capacitor bank.
Stator of three phase induction motor creates Rotating Magnetic field.But why not Transformer?
long form of CT
3 Answers MSETCL Maharashtra State Electricity Transmission Co Ltd,
in transmission line 11kv is step up or step down? why?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)