Why we use shunt coil in breaker??????????
Answers were Sorted based on User's Feedback
Answer / i.senthil kumar
if
if it is happened any earth fault or short circuit to
energized the shunt coil,immediately tripped the ACB
| Is This Answer Correct ? | 18 Yes | 4 No |
Answer / md waseem khan
Shunt trips are devices used for the remote
instantaneous opening of the air circuit
breaker. They are generally controlled trough
an N/O type contact. The actual offer of
shunt trips proposes two supply voltages
(110 V and 220 V), both compatibles with AC
and DC currents. The shunt trips are already
equipped with a special fast connector, to
be directly inserted into auxiliary contacts
block. An auxiliary contact is connected in
series with the coil, cutting off its power
supply when the main poles are open.
| Is This Answer Correct ? | 9 Yes | 2 No |
Answer / gopal
We can't open relay contacts With out shunt trip coil. So it is essential to open circuit breaker during fault condition.
| Is This Answer Correct ? | 1 Yes | 3 No |
Answer / s.krishnamoorthy
the shunt coil 3phase supply any one phase not come that
will triped acb.
| Is This Answer Correct ? | 2 Yes | 19 No |
as per BIS supply voltage in India is ......
What are the difference between normal application Transformer and Solar application Transformer?
Why secondary of a CT in a power system acts as an open circuit after core saturation?
how to find three phase complex power in per unit and MVA?
What is the permissible value of earth resistance and as per which standard / act / rule ?
What does a permanent magnet generator do?
how to calculate the ct burden?
ELECTRICAL DRIVES: can a motor load system with passive load torque can have equilibrium speed in second quadrant
What's mean HVF & HAF in Vacuum Circuit Breaker?
0 Answers Gandhi Institute of Technology and Management (GITAM), Hyundai, Jayam Engineering Works,
what is meant by peak load
what is meant by switch fuse unit ?
3 Answers Thermal Powertech Corporation India Ltd TPCIL,
How to find Cable size? Caterpillar generator produce (Two generators) 127*2=254 amp at 11 kv . What would be the cable size (XLPE) to supply 256 amp at 11 kv? Air or surrounding Temperature is 32 degree C. Cable will go under ground at 2.5 feet depth. Group Rating Factors is 3 cables. Clearance between cables is 7 cm. Soil Temperature (Ambient) 28o C Soil Thermal Resistivity is 1.2 K.m/W I would like to use 3 separate single core instead of using 3 core cable. Some says I should use three separate single core 120RM cables. Some says 70RM .some says 95. I m totally confused. Is there ant specific rule to determine cable size? What would be the LT cable size to flow 500 Amp current? Ifte My e mail address is ifte13@yahoo.com Anyone please send me the answer to my e mail address, i will be very glad.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)