why we avoid parallel operation of diesl generator?
Answers were Sorted based on User's Feedback
Answer / goodwhisher
to lokesh
this site is very good for good engineers,please dont spoil
it please,it's no a funny matter.
dont answare if you dont know,please.
Is This Answer Correct ? | 9 Yes | 0 No |
Answer / johnson m.c.
1) Potential of both alternators must be equal. Both must
have same output voltage.
2) Phase sequences of both the alternators must be same.
The RYB phases of one alternator must
be connected the RYB phases of the other alternator.
3) Frequency of both the alternators must be equal. If one
alternator is operating at a frequency of 49
Hz and the other one is delivering voltage at 51 Hz, then
load on the second alternator would be
more. We have to increase the speed of the prime mover of
the first alternator in order to effect a
match in frequencies.
4) Phase angle of voltages of the two alternators must not
be more than 10 degrees.
5) During manual operation of synchronization, the load
could witness kick (which is a peak of
current). This kick could burn the alternators on the load.
The only solution is the use of automatic
synchronisation equipment. However, expert engineers could
close the CB of the second
alternator when the difference of phase angle between the
two voltages is 2 degrees.
6) The alternators must share loads with respect to their
ratings.
7) The alternators must have similar voltage drooping
characteristics.
8) The engines of the alternators must have similar
governor characteristics;
Is This Answer Correct ? | 10 Yes | 4 No |
Answer / rajanikant
lokesh why you want to spoil this site this is very good
site for engineers
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / lokesh ranjith
because in parallel operation when electricity fails all Dg
sets will gets on even if the load is less also
There will be more diesel consumption
if we run the dgsetd solo mode we can give 80% load can get
goog efficiency
Is This Answer Correct ? | 2 Yes | 20 No |
Is only insulation the difference between High voltage and Medium voltage cable?
is that any software calculator to calculate the size of cable
What are types of encoders?
19 Answers ITC Infotech, UFO, Wipro,
What is an iron loss or core loss pi?
How can calculate thermal overload in relay?
When to use Oil Transformer type and When to use Dry type? What is the difference between both?
circuit diagram of trip circuit supervision relay
List out the different frequency domain specifications?
How to megger test 11 kV cable and the acceptance IR value
What is meant by operating sequence of VCB : 0–0.3sec.–CO– 3min.-CO
I have been using an 600VA with 0.6 p.f UPS with my desktop which has 450W power supply unit. Can anyone explain how can this happen . Because the output of the UPS is 360W (600*0.6) (<450W)
What will happen if we give the 3 phase supply to the rotor of slipring induction motor?