What is the Polarisation index value ? (pi value)and
simple definition of polarisation index ?
Answers were Sorted based on User's Feedback
Answer / shane e.
It is the ratios of of insulation resitance on a DC hi-pot test over 10 minutes. If less than 1 insulation is surely breaking down.
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / lovy
Polarization index is an indirect method of testing which may mislead about healthiness of transformer insulation
so instead of pi , capacitance and tan delta should be measured for keeping a correct check on insulation
Is This Answer Correct ? | 13 Yes | 15 No |
Answer / josephat murusura
PI is the ratio of the 10minutes megger value to that of
the 1 minute.The minimum acceptable value is 2.Any value
below 2 is not good enough for the operation of the
electrical machine[motor or transformer]& it indicates that
the winding insulation has detoriated.
Is This Answer Correct ? | 3 Yes | 13 No |
Answer / karthik
It's minimum acceptabce value depends on the class of
insulation also. Minimum recommended value IR(60 sec)/IR(15
sec) should be 1.3 for all classes of insulation.
Is This Answer Correct ? | 6 Yes | 18 No |
Answer / sandipan sarkar
it is ratio of insulation resistance (IR)for 10 minutes to
insulation resistance for 1 minute.
it should be 2.5
Is This Answer Correct ? | 35 Yes | 57 No |
Why we use parllel operation of alternator
Is KCL applicable for close circuit?
what is the abbreviation & meaning of UI charges
Which types of gate insttaled in static switch. Please give me answer.
two phases with neutral supply can be taken in 3C X 10 sq.mm cable .
All tape of electrical questions Answers tape of motor transformer e.o.t crane
0 Answers Afcons, Honeywell, Manlift, SIMS,
How to calculate KW what is the formula for KW.
WHY TRANSFORMER RATING IS MENTIONED IN KVA RATHER THAN KW
what is the use of surge suppresser in 33 KV incoming panel. where it must be installed,inseries with incoming cable surge suppresser must be at incoming of the breaker are outgoing of the breaker
if two transformers are parallel & both have fault short ckt. impedance of 50KA in each case will it increase or decrease show example?
for 644KW load which MCCB should i use
Calculation for the adequacy of 380 KVA neutral earth flat size