110 KW MOTER DOL STATER 240SQ.MM CABLE MOTER AND STARTER
DISTANCE IS 110 METER WHAT IS VOTAGE IN MOTER END AND
SYSTEM VOTAGE IS 415 V HOW I CAN CALCULTE
Answers were Sorted based on User's Feedback
Answer / capseee
Its depends on the cable manufacturer and type of cable
(XLPE/PVC), type of conductor(AL/CU), system
(underground/overhead) etc. Also you have to consider
derating factors like temperature,gap betwwen cables,
distance between cable trays etc(thease details are
provided in the catalogue).
Also the manufacturer provided mv/amp/km details from that
you can calculate the voltage drop. As per standard the
drop at receiving end should be +/- 3% of sending end
voltage.
| Is This Answer Correct ? | 1 Yes | 3 No |
Answer / m s rana
Its depends on the cable manufacturer and type of cable
(XLPE/PVC), type of conductor(AL/CU), system
(underground/overhead) etc. Also you have to consider
derating factors like temperature,gap betwwen cables,
distance between cable trays etc(thease details are
provided in the catalogue).
Also the manufacturer provided mv/amp/km details from that
you can calculate the voltage drop. As per standard the
drop at receiving end should be +/- 3% of sending end
voltage.
But it is not engineering to run 110kw motor run to DOL
Starter It IS VERY HIGH LOAD & LONG DISTANCE higher losses
| Is This Answer Correct ? | 2 Yes | 4 No |
When connecting a loaded powerplant to the Huge grid,what are the factors to be considered and how the VAR flow will affect the system?
what is the mechanism of operation of brushless dc motor why is it more wexpensive then ordinary permanent magnet motors
circuit breaker is ...............connected with circuit
How will you define capacitance?
what is consequences of neutral and earth connect?
what is the function of garing capacitir in SF6 circuit braker?
can we use engine degreaser for electrical motors?
Is there any decided or standard frequency to check the meager testing of transformer, DG set, LT Panel in the industries in a year. I means how many times we should be check the same.
how to calculate load if i have three phase & single phase connection from power transformer( in term of kw & kva).can i take single phase load/3 for total kw calculation
Instead of single phase(220), if apply Phase to phase supply (eg: for lighting fixture). what will be the power formula? what will be the volt and current value? please explain me with some example.
how to calculate sizing of NGTR (Transformer rating,Loading resistor value and Current rating of resistor) and what is the X/R ratio. Details : 11kV,Capacitance 1.73532 micro farads,40kA for 1sec.
1 Answers Bhel, Indorama, Power Grid,
How to calculate load taken by a cable?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)