110 KW MOTER DOL STATER 240SQ.MM CABLE MOTER AND STARTER
DISTANCE IS 110 METER WHAT IS VOTAGE IN MOTER END AND
SYSTEM VOTAGE IS 415 V HOW I CAN CALCULTE
Answers were Sorted based on User's Feedback
Answer / capseee
Its depends on the cable manufacturer and type of cable
(XLPE/PVC), type of conductor(AL/CU), system
(underground/overhead) etc. Also you have to consider
derating factors like temperature,gap betwwen cables,
distance between cable trays etc(thease details are
provided in the catalogue).
Also the manufacturer provided mv/amp/km details from that
you can calculate the voltage drop. As per standard the
drop at receiving end should be +/- 3% of sending end
voltage.
| Is This Answer Correct ? | 1 Yes | 3 No |
Answer / m s rana
Its depends on the cable manufacturer and type of cable
(XLPE/PVC), type of conductor(AL/CU), system
(underground/overhead) etc. Also you have to consider
derating factors like temperature,gap betwwen cables,
distance between cable trays etc(thease details are
provided in the catalogue).
Also the manufacturer provided mv/amp/km details from that
you can calculate the voltage drop. As per standard the
drop at receiving end should be +/- 3% of sending end
voltage.
But it is not engineering to run 110kw motor run to DOL
Starter It IS VERY HIGH LOAD & LONG DISTANCE higher losses
| Is This Answer Correct ? | 2 Yes | 4 No |
In iduction motors the current is higher than normal for both the cases when the voltage appllied is more than the rated as well as less than the rated, why?
what is the saturation point of crgo lamination.
what is the Excaste meaning of CT Saturation?? 10 P 20, 15 VA, what is the meaning of 10, & 20. if the CT polarrity changed what will happened?? what is the differece between measuring CT & Protection CT?? what is the Saturation Point of measuring CT & Protection CT??
What is power factor? How to improve Power factor? draw a circuit diagram showing the connection of power factor improvement equipment to the electrical instillation.
how the diesel generator maintain the rpm when the generator loaded varies from 10% to 70% immediately?
What is the range of the stator resistance of 3 phase induction motor?
A group of machines (wind turbines) connected with 33KV feeder and each machines are having individual VCB. The 33KV feeder connected with 110KV/33KV substation. The 33KV feeder tripped by over current at Substation and fault recorded at Substation as OC-R&Y phase. Same time the group of machines VCB tripped by over voltage, the fault recorded voltage was above 66KV by numerical Under/Over voltage relay. While grid drop time, this much of voltage hike is possible?
pf of synchronius motor is unity, is it axact(=one) value. ?
What is the basis for framing the rules of block diagram reduction technique?
what is the use of reactive power
What is thermal overload relay
HOW TO MEASURE AC VOLTAGE BY USING GALVANOMETER?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)