Answer / capseee
Its depends on the cable manufacturer and type of cable
(XLPE/PVC), type of conductor(AL/CU), system
(underground/overhead) etc. Also you have to consider
derating factors like temperature,gap betwwen cables,
distance between cable trays etc(thease details are
provided in the catalogue).
Also the manufacturer provided mv/amp/km details from that
you can calculate the voltage drop. As per standard the
drop at receiving end should be +/- 3% of sending end
voltage.
Is This Answer Correct ? | 1 Yes | 3 No |
Answer / m s rana
Its depends on the cable manufacturer and type of cable
(XLPE/PVC), type of conductor(AL/CU), system
(underground/overhead) etc. Also you have to consider
derating factors like temperature,gap betwwen cables,
distance between cable trays etc(thease details are
provided in the catalogue).
Also the manufacturer provided mv/amp/km details from that
you can calculate the voltage drop. As per standard the
drop at receiving end should be +/- 3% of sending end
voltage.
But it is not engineering to run 110kw motor run to DOL
Starter It IS VERY HIGH LOAD & LONG DISTANCE higher losses
Is This Answer Correct ? | 2 Yes | 4 No |
What is the Difference Between resistance and resistivity?
what is an rmu?its circuit diagram.functions
14 Answers CP Bangladesh, Emrill, NDPL,
What is meant by reverse polarity and how it can be fixed?
how to reduce humming noise in transformer?
why we have to do tan delta test of the transformer oil???
If you don’t have coal, salt and copper, then how would you earth your connection temporarily at a camp site.?
i want to syncronise 5 nos of DG. How? pls reply
what is closing resistor in circuit breaker? why it used?
what different in delta & star connection in motor?explain
5 Answers Bhushan Power Steel, Hyundai, KPCL, L&T,
purpose of flux relay for turbo generator in power plant
Define transfer function?
Main CT ration is 400/5, meter CT ratio is open type: -/5A. What is the Multiplying factor of the meter, considering same PT ratio.