110 KW MOTER DOL STATER 240SQ.MM CABLE MOTER AND STARTER
DISTANCE IS 110 METER WHAT IS VOTAGE IN MOTER END AND
SYSTEM VOTAGE IS 415 V HOW I CAN CALCULTE
Answers were Sorted based on User's Feedback
Answer / capseee
Its depends on the cable manufacturer and type of cable
(XLPE/PVC), type of conductor(AL/CU), system
(underground/overhead) etc. Also you have to consider
derating factors like temperature,gap betwwen cables,
distance between cable trays etc(thease details are
provided in the catalogue).
Also the manufacturer provided mv/amp/km details from that
you can calculate the voltage drop. As per standard the
drop at receiving end should be +/- 3% of sending end
voltage.
Is This Answer Correct ? | 1 Yes | 3 No |
Answer / m s rana
Its depends on the cable manufacturer and type of cable
(XLPE/PVC), type of conductor(AL/CU), system
(underground/overhead) etc. Also you have to consider
derating factors like temperature,gap betwwen cables,
distance between cable trays etc(thease details are
provided in the catalogue).
Also the manufacturer provided mv/amp/km details from that
you can calculate the voltage drop. As per standard the
drop at receiving end should be +/- 3% of sending end
voltage.
But it is not engineering to run 110kw motor run to DOL
Starter It IS VERY HIGH LOAD & LONG DISTANCE higher losses
Is This Answer Correct ? | 2 Yes | 4 No |
Write the analogous electrical elements in force voltage analogy for the elements of mechanical translational system.
How many types of Transformer testing..
what are clipper and clamper circuits?
how to calculate the starting current of a motor? gopal
What is plc.
what happens when we give ac supply to the dc motor?and why?
What are types of encoders?
19 Answers ITC Infotech, UFO, Wipro,
How many straight through joint is permissible in single core 33kv XLPE cable for a length of 985 mtr.
if we convert Ampers into kva,which one formula use by us,pls tell me?
what is LSR?
how to calculate cable size in diffrent loads?
what is mean by VCB colour code..???