how to calculate the kw, Amps consumed by a capacitor,
give me the formula for KVAr into capacitance,KVAr into KW
& KVA, Amps

Answer Posted / pugalenthi.s

Amps can be calculated by = KVAr / (V line to line * 1.732
for three phase.
KW can be calculated by = V * I * 1.732

Is This Answer Correct ?    8 Yes 4 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

How to use computer cpu ups use for home inverter circuit board

1478


What happens if the negative to earth voltage is greater than positive to earth voltage in the battery of substation?

1284


what ispositive, negative, zero sequence impedence?

1750


How much should be the load percentage for 15kva Inverter and Iinut & I output load with Calculations

1797


what is under coal gassification?

1792






What are the internal and external faults?

801


What is oscillator circuit?

853


when we design electrical schemes of 11/.415kv distribution..wen and were should we show the relays??what is the function of it?for example..we place EFR Relay CT between transformer neutral link and transformer earth.Like this what are the other type of relays we should use?why?where?Explain please..Thank you

1556


On what cycle does thermal power plant operate?

830


how to identify vector group of three phase transformer by voltage method?

1339


what is difference between isolation and ultra isolation transformer?, what is the method of testing ?

4040


how calculate gd2 of ht motors

2027


what are the effects when a salient pole alternator is run at high speed like 3000 r.p.m?

2137


3 phase Motor will be given 2 phase after 2 to 5 second we given 3rd phase so Motor Run sum-time in forward or sum time run reverse direction. All time phase sequence is not change. Why motor run in reverse direction? Please Explain........

1672


What is meant by vector group

2128