Answer / krishna

proportion control function is to maintain constant offset
between set point and process variable .but it cannot remove
the offset. it makes the p.v to oscillate between high and
low limits.

There are two things required for calibrating control valve
1)pneumatic tester ( signal :0.2 to 1kg /cm2
)
2) air supply source according to design of valve.
initial for 0.2 kg.cm2 valve should be (open or close )
according to ATO ATC) )
THEN CHECK POSITION AT 25 50 75 100 % OF VALVE ACCORKING TO
SIGNAL TUNE WITH POSITIONER

Is This Answer Correct ?    20 Yes 1 No

1.what is the role of proportional comtroller in pid controller?2.How do u calibrate the control v..

Answer / www.islamqa.com

Actually we can make it simple:

# P:
it's a controller gain which modify the controller o/p
proportional to the error.

# I:
it's a controller gain which modify the controller o/p
proportional to the integral of the error.

# D:
it's a controller gain which modify the controller o/p
proportional to error rate of change.



We have 4 parameters in our control loop to focus on:
1 - the rise time: the period of time during which the pv
get 90% of the desired sp value
2 - max overshoot
3 - settling time: the period of time during which the pv
get the desired sp value and saturate.
4 - error/offset

we can get it clear from this pic:
http://controls.ame.nd.edu/ame437/S2003/hw1/specifications.j
pg

Now we will take a look about the effect of each controller
gain on these parameters:

# P gain:
decrease rise time
increase max.overshoot
increase settling time
decrease error (but not eliminate)


# I gain:

decrease rise time
increase max.overshoot
increase settling time
eliminate error.


# D gain:

no effect on rise time
decrease max.overshoot
decrease settling time
decrease error.

the previous is guidelines to be in background while
dealing with PID,but they are not sharp limits.

Regards,

Ahmed Sabry
Control and Instrumentation Engineer
GPC - General Petroleum Company
ahmedsabry.online@gmail.com
CELL.: 00 2 0121367310

Is This Answer Correct ?    10 Yes 0 No

1.what is the role of proportional comtroller in pid controller?2.How do u calibrate the control v..

Answer / prashant

proportional function is take place an action to maintain
the pv proportionaly to error in p.v . but an offset error
is sustained , that will be reduced by integral funtional.


calbration of control valve :::
1. check the pneumatic pressure of regulator
2. give the 4-20 ma to check the strock of c/v
3. if storck is not achieving then adjusted by zero
& span adjustement

Is This Answer Correct ?    9 Yes 4 No

Post New Answer

More Instrumentation Interview Questions

WHAT IS THE DIFFERENCE BETWEEN A TRANSMITTER & A SMART TRANSMITTER.

8 Answers  


what is beta ratio?

3 Answers  


Could anybody tell how much amps will a single input to plc will consume?

1 Answers  


what is relation between electronics&instrumentation

4 Answers   Hindustan Zinc,


What is cavitation. what is the effect of it on control valve and how is it prevented.

1 Answers   ADMA OPCO,






-/5A. What is the meaning and limitations of this in energy meter constant. It is a 3 phase LT Energy Meter. If this Energy Meter is connected through a CT of ratio 200/5 Amps, then what is the multiplying constant and how its will be calculated.

0 Answers  


In the field and in the control room different power supplies if used How to handle the ground

1 Answers   ITC Infotech,


how to check control valve was passing?how to check online?

3 Answers  


How will you calibrate an Absolute Pr.Transmitter of range 400mmHg absolute ?

0 Answers   CCIE,


pressure switch range 0 to 2bar.i have to install from ground level to 5 meters height.what is the formula the to increse the range ? and every 1 meter how much pressure should be add ?

3 Answers  


difference between span and range

3 Answers   IOCL,


how micro-processor and micro controller different from architecture

3 Answers   Bhushan Power Steel,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4452)
  • Electrical Engineering Interview Questions Electrical Engineering (16637)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)