Answer / kannu
generation:11-16.5kv
transmission :132-765kv
distribution: 230v,415v
| Is This Answer Correct ? | 14 Yes | 2 No |
Answer / ramanjaneyulu
genaration:11kv
transmission: 400kv-33kv
distribution:11kv-415,230v
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / prashant
the above ans is write though i wud like to add 230 V i the
distribution
| Is This Answer Correct ? | 8 Yes | 6 No |
Answer / arul
Generation : 11kv
Distribution. : 440v: 240v
Transmission:440kv ; 33kv; 765kv
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / azarudeen
Generation : 11 KV - 20 KV(20 KV for 600 MW generator)
Transmission : 33 KV - 765 KV(765 KV is DC)
Distribution : 230V - 33 KV
| Is This Answer Correct ? | 2 Yes | 3 No |
Answer / nagarjunacharya
gen 11kv-16.5kv tXssion33kv765kv distribution 33kv-
22ov
| Is This Answer Correct ? | 0 Yes | 2 No |
If age of Raju is 20% less than Sanju,then age of Sanju is how many % more than Raju
why we measure output of transformer in kva?
what is the different between bus section and bus coupler
how to calculate the multiplication factor in HT incomer trivector meters
9 Answers Dalkia, Getco, Gujarat Energy Transmission Corporation Limited GETCO,
If a manufacturer decribes a power supply transformer as providing a secondary voltage of 24 volts when connected to a 240 volts supply, do you think they are refering to the full load or no load secondary voltage?
We know that, in case if there is a faulty insulation,or sc, the current is bypassed to earth through the earth wire that has low resistance.Actually, what will happen to that current that flows through gnd?In that case,if we come in contact with that faulty appliance, wont that current flow through us as we form a closed path by standing in gnd?Is grounding a safety measure?
why transformer rating in KVA or MVA instead of KW n MW??
why elcb used in circuit
HOW TO FIND OUT 1. LINE CURRENT, 2. PHASE CURRENT IN AN ALTERNATOR / TRANSFORMER WHICH IS FEEDING A I)STAR LOAD ii) DELTA LOAD, USING A CLAMP METER. NORMALLY WHEN WE USE CLAMP METER IN A DG SET THEN WHAT DO WE GET?? PHASE CURRENT OR LINE CURRENT.
How to know any size of cable if there are not written on cable? Answer must be theurical not by experience.
Why Earthin is not required in Xformer primary side when it is in Star / star?
1.what is the funtion of chiller primary & scondary pumps. 2.what is the use of distribution lines & Types. 3.what is the use the thermal power stations & how much capacity.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)