what is the significance of tan delta testing?explain the
theory?
Answers were Sorted based on User's Feedback
Answer / a.r.shah
Tan Delta is an effective tool in determining the
insulation condition of power cables using a VLF-TD System
Tan Delta measures the resistive component of a cable
system; a perfect cable is all capacitance and has no
resistance. The resistive component is caused by voids in
the insulation, electrical trees, water trees etc. The
resistive element causes the current not to lead the
voltage by 90° (something less) This is difference in angle
(less than 1° ) is the loss angle. The tangent of this loss
angle is the Tan Delta / or the tangent of the loss angle.
Thanks for Marking this Answer
Is This Answer Correct ? | 29 Yes | 4 No |
Answer / er. ankush miglani 9718151073
Tan Delta is an effective tool in determining the
insulation condition of power cables using a VLF-TD System
Tan Delta measures the resistive component of a cable
system; a perfect cable is all capacitance and has no
resistance. The resistive component is caused by voids in
the insulation, electrical trees, water trees etc. The
resistive element causes the voltage not to lead the
current by 90° (something less) This is difference in angle
(less than 1° ) is the loss angle. The tangent of this loss
angle is the Tan Delta / or the tangent of the loss angle.
Is This Answer Correct ? | 30 Yes | 12 No |
Answer / koushik goswami
Ideally an insulation (be it across a cable or a electrical
switch gear) should be of infinite resistance. That is
ideally if voltage is applied across insulation no current
should pass through (considering resistive current only).
Now there is another aspect of an insulation. An insulation
is also a capacitor (two plates seperated by dielectric)
and hence there must be some current (opf course ac
current) that will flow if voltage is applied acroos
insulation (this is capacitive current). Now the ration of
the resistive current (which shoud ideally be zero) and the
capacitive current is called loss tangent or tan delta and
is measurable. So if tan delta is measured we are actually
get an idea of the resistive current through the
insulation. A high tan delta indicates high resistive
current and that means insulation is detoriating.
Is This Answer Correct ? | 20 Yes | 3 No |
Answer / m r bhanderi
Ideally an insulation (be it across a cable or a electrical
switch gear) should be of infinite resistance. That is
ideally if voltage is applied across insulation no current
should pass through (considering resistive current only).
Now there is another aspect of an insulation. An insulation
is also a capacitor (two plates seperated by dielectric)
and hence there must be some current (opf course ac
current) that will flow if voltage is applied acroos
insulation (this is capacitive current).& IDEAL CAPACITIVE
CURRENT IS ALWAYS 90 DEG AHEAD THAN VOLTAGE AS PER R-C
CIRCUIT VECTOR DIAGRAM.BUT DUE TO AGING EFFECT &
DETORIATION OF INSULATION , CAPACITIVE CURRENT IS SLIGHTLY
LESS THAT 90 DEG & ONE ANGLE CREATED BET IDEAL CAPA.
CURRENT & ABOVE SAID CURRENT IS CALLED TAN DELTA ANGLE.
HENCE WE CLEARLY SAY THAT TAN DELTA IS the ration of
the resistive current (which shoud ideally be zero) and the
capacitive current is called loss tangent or tan delta and
is measurable. So if tan delta is measured we are actually
get an idea of the resistive current through the
insulation. A high tan delta indicates high resistive
current and that means insulation is detoriating.
Is This Answer Correct ? | 14 Yes | 1 No |
Answer / veena nair
tan delta testing is usally carried out to check the
healthiness of insulation.so this testing is usally carried
out in cb ,ct, bushings etc ,for all these equipements one
standard value will be there,for breakers this value will
be 0.00073, if any devation in this value we have to
suspect about it insulation healthyness.
Is This Answer Correct ? | 22 Yes | 10 No |
Answer / manish yadav
tan angle is the ratio of resistance current and
capacitive current ..it is used to estimate the life of
insulation by comparing periodical tandelta value of the
same insulation..pure insulation has only capacitive
current but with the insulation deteriorationor cavity
formation(may occur due ambient condition temp or cont.
over current flow) resistance is added hence resistive
current increase wich leads to increase in tandelta value..
Is This Answer Correct ? | 5 Yes | 2 No |
Answer / mirza faiz baig
In general for electrical component, Ten delta means that the tangent value of insulating material. what is tangent value of IM? it is nothing but the dissipation factor. what is dissipation factor? The ratio of Power/ Voltage-Ampear (W/VA). so finally in simple words Tan delta testing is nothing but to find out the health of insulation OR insulating material.The test can be performed on Cables, power TR's or any electrical component.
hope i am able to answer
Is This Answer Correct ? | 3 Yes | 2 No |
The inexpensive way to improving energy efficiency of a motor which operates consistently at below 40% of rated capacity is by _____.
what is dielectric heating
what is value of Jin transformer
why crgo core is used in transformers?
What is Skin effect in Cable?
Dears we deal in Chemical are Plate earthing. Kindly call if any requirement and questions. Tech Earth Solutions Mohit Verma 8791071007
how we can improve power factor from 0.8 to 0.85 or 0.9 & how we identify its either lag or lead ? thank you
who many types of fire explane with exmple
why not feeling shock while touching rotor shaft of induction motor during running condition? during running condition emf induced in rotor.
What is the difference between isolators and electrical circuit breakers?
What are the different sign conventions used in electric circuits?
pls send me some of the solved question booklet of Junior Engineer -2 (ELE) in RRB