how to calculate capacitor bank value to maintain unity
power factor plz xplain with some suitable xample?
Answers were Sorted based on User's Feedback
Answer / er. ankush miglani 9718151073
KVAR= KW(TAN(COS(-1)#e)- TAN(COS(-1)#d) )
#e= EXISTING P.F.
#d= DESIRED P.F.
Is This Answer Correct ? | 35 Yes | 3 No |
Answer / shalini.b
capacitor bank value is calculated in KVAR
From Power Triangle,
KVAR = Sin(phi) * KVA
Desired Power factor = 0.96 (say)
cos(phi)=0.96
phi = cos(inv)0.96
phi= 36.86
Sin(phi)= 0.28
If the transformer rating is 1250 KVA (say)
KVAR = 0.28*1250
= 350
Is This Answer Correct ? | 22 Yes | 8 No |
Answer / maen drawish
The proper calculation for cap. bank it depends on the
desired & initial/ existing cos-phi.
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / skumar
I don't know the correct formula. But in practical we
applying 30% of our full load(i.e transformer capacity).
Is This Answer Correct ? | 4 Yes | 7 No |
How PSV sizing being done
Convert a star connected network into a delta connected network.
what is the difference between home inverter and online ups?
how gen. load increase or decrease ? what happen with gen on that time
How do you commission a power Transformer?
Explain the grounding concept adapted in aircrafts?
different b/w counter poise and ground wire
Can you explain the phase displacement between primary and secondary of power transformer of any vector group(for ex)?
how to calculate the distance relay faulty zone?pls explain?
What is the advantage of Neutral graunding transformer insted of Neutral graunding Resistance in generating station explain briefly.
Pls Breifly explain about UPS (Inverter,Reserve,Rectifier,Float voltage,Boost voltage).
If you touch power transformer........ Then , in your body current will flow or not...?