why is it that the HT motors & motors having very low kW
rating(<1kW) have windings connected in STAR, whereas the
motors having in between kW ratings have DELTA connected
windings??

Answers were Sorted based on User's Feedback



why is it that the HT motors & motors having very low kW rating(<1kW) have windings connect..

Answer / avdhesh

The basic differance in star and delta connection is that
in delta connection voltage across the winding is line
voltage (V-line) and in star connection it is phase voltage
(V-line/1.73). Same way current in each winding in delta
connection will be (I-line/1.73) and in star connection it
will be line current(I-line). Now to design any motor one
has to take cost of insulation as well as copper.In delta
connection you need higher insulation and in star
connection you need thick conductor to cary high current.

For HT motors current is less as voltage applied is high
hence to reduce insulation cost star connection is made.

For higher rating LT motors since current is high delta
configuration is recommonded.

If we do not follow above than cost and size of machine
willbe increase.
Hope this is the answer of your question.

Is This Answer Correct ?    6 Yes 0 No

why is it that the HT motors & motors having very low kW rating(<1kW) have windings connect..

Answer / saurabh

During Design it self it is take in consideration
As Power = Torque x Angular Velocity(RPM)

So for same RPM(say 1500 rpm), for Same Input Voltage

1) In star connection Torque will be less hence Power
output will b less

2) In Delta Connection Toruqe will be More hence Power
output will b more

as far as HT motors are concern, in order to limit inrush
current star connection could b given.

Is This Answer Correct ?    6 Yes 3 No

why is it that the HT motors & motors having very low kW rating(<1kW) have windings connect..

Answer / gunasekaran

that is not economical why we r going to high voltage for
high KW rating for reduce the loss. delta connected load is
giving 3 time power output than star.

Is This Answer Correct ?    3 Yes 0 No

why is it that the HT motors & motors having very low kW rating(<1kW) have windings connect..

Answer / shyamal

Thanks Avdhesh for the answer...
Can you tell me whether one can operate star connected motors
with delta connection & vice versa?

Is This Answer Correct ?    1 Yes 0 No

why is it that the HT motors & motors having very low kW rating(<1kW) have windings connect..

Answer / kanth.g

Actually the question is not in Proper way try to get it
right.

Is This Answer Correct ?    1 Yes 6 No

Post New Answer

More Electrical Engineering Interview Questions

How to calculate cable size by using load.?? Any formula...

0 Answers  


how we masure a cuurrent?

5 Answers  


When do you use a VFD motor?

1 Answers  


In EDO ACBs what is a purpose of closing coil and motor, what is the operation of these devices are they inetconnected. means if we give supply to motor and by BCS we charge Closing coil,what exact is operation is and how it charge a spring of ACB. Sir if anybody has an wiring diagram please send me the link to operate and EDO breaker.

0 Answers   PCE,


Why all voltage levels are the multiples of 11KV?

10 Answers   KSEB,






How do i perform grounding of star point of Genset (400V) for making connection with step up transformer of DELTA-DELTA (400V to 20KV) ? while Genset itself has its own neutral and grounding bus bar inside genset breaker box whereas we have another neutral and grounding busbar in synchronizing panel next to genset at maximum distance of 6meter, would someone pls advice if we can only perform neutral grounding in synchronizing panel or should we ground neutral on both places inside genset breaker box and synchronizing panel.

0 Answers   Allied Group,


why we use 11 kv 22 kv and so on ?

1 Answers   Air Force,


what is the basic difference between fan and home motor if both have single phase induction motor?

4 Answers   Engineers India Limited,


From an electrical motor & electrical generator, which has more efficiency & why?

1 Answers   Sahi,


what are the basic insulation levels & what its Unit

0 Answers  


STATE AND EXPLAIN SUPER POSITION THEOREM.

3 Answers   ABB,


Testing report of Earthing of 3.15 MVa PTR.

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)