In neutral the current will flow or not?
Answers were Sorted based on User's Feedback
Answer / abc
in balanced condition no current flow through neutral but
in unbalanced condition current flows thru it
| Is This Answer Correct ? | 91 Yes | 7 No |
Answer / pratheesh
In 3 phase with neutral wire system, if the loads on all
phases are equal, there will not be any current flow in
neutral.
But if the loads on any phase/s are not equal compared to
others, there will be some current flow through neutral.
| Is This Answer Correct ? | 51 Yes | 5 No |
Answer / abdul wajid
Current will only flow in neutral when there is unbalanced
load otherwise in balance load no current will flow in
neutral
| Is This Answer Correct ? | 26 Yes | 2 No |
Answer / faizal
question is current flow in neutral rit.
so we can start from single phase. there is phase and neutral wire and we are connecting this 2 wire across any load ok.
phase wire carries in coming current and neutral wire carrries outgoing current. but when we touch neutral wire we wont get any electrical shock dats why every one have confusion. the answer is current is always flow through low resistance path. neutral wire potential is always zero and it is connected to earth in substation. so while we touching the neutral wire current has 2 path. one is through our body to earth , second one is through neutral wire . our body has some resistance. so obvoiously current wont flow through the resistance path in this case.
| Is This Answer Correct ? | 16 Yes | 0 No |
Answer / kapil n.bahadure
The current will flow in neutral when circuit have in
unbalanced condition in three phase system.The magnitude of
current & impedance valeu is not same then retern current
flow in neutral wire for circuit comleted.
The single phase system neutral is required for circuit
complete.when circuit comleting then current flow by
neutral wire.
| Is This Answer Correct ? | 9 Yes | 2 No |
Answer / srinivasa kc
The current always flow from higher potential to lower potential i.e, from phase to neutral(In a single phase circuit).as we know the T/F sec is star connected i.e, neutral wire is grounded in the T/F placing point, so all the current flows from phase through load to neutral(The return current always flows through the neutral for closing the circuit path) hence we cant feel the shock even if we touch the neutral wire because neutral is at ground potential(i.e, current always flows through the low resistance path)
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / ramendra shukla
In Y- connected load (3 phase)
1) If Ir= Iy=Ib then In=0 (Symetrical /balance)
2) If Ir#Iy#Ib ; then In=x (Unsymetrical/unbalanced)
where; Ir,Iy,Ib &In are phase &Neutral current
respectivelyand also #is is not equal
3)but in case of Single phase looping the avilability of
current will be.
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / ashish saxena
under unbalance condition of phase current will be flow
through the neutral .otherwise it will be remain zero..
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / deepu electrical supervisor
Yes, there will be current flow in the neutral wire based on the unbalanced condition. We used 3.5 core cables for power circuits and high gauge copper as its earth. In the case of lighting circuits we used 4 core cables cables and less gauge copper wire for its earth. Normally, the neutral point is properly grounded from the transformer neutral by means of copper plates, hence it is at zero potential. We know current flow from high potential to lower potential, so when we switch on the load there will be a tendency of current to flow from phase to neutral but the power is consumed by the load based on the ratings and its types. But at balanced load condition there will be very less current flow on the neutral wire because the load consumes full current. But when unbalanced fault occur there will be return current flow in the neutral wire to the source. In this case the circuit get tripped by circuit breakers.....
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / babu
yes,,current is flow from neutral when load is unbalance in
3 phase.
| Is This Answer Correct ? | 1 Yes | 0 No |
For a certain load i need 100kw load ,In that case what rating mccb should i use?
What does OHB stand for in specifications for circuit breakers, especially found in SF6 circuit breaker?
Is KCL applicable for close circuit?
Hello sir. if u have electical engineering exam paper then plz mail me at bhumika_1187@yahoo.co.in. i m appearing exam for HPCL.
what is differnce btwen lll and lllg faults
Power Factor Correction Panel (Manual & Automatic)
can we start mulitple 3 phase induction motors with common starter?
How npn and pnp transistor works
Dear all: Recently we got a question about Interface between PMS and SAP-PM.once we got a update message from PMS.we should set the deletional flag for functional location in SAP system.Is there any FM or BAPI to use?There are only functional location create and change provided by SAP. Best regards!
what is skin effect and why is it absent in DC systems
What are the main advantages of generalized error co-efficients?
what is the acceptable limit value for Desolve Gas Analysis/
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)