How to select the Cable size for 550 Amps Load without
seeing the cable Catalogue?
Answers were Sorted based on User's Feedback
Answer / ramesh kumar k
the size of the cable depends upon the material used in the
cable...
if u go for copper cable... the copper has got the current
carrying capacity of 2A/sq.mm continuously with out
overloading effect. so if you want for 550A,
550/2 = 225 sq.mm copper cable u have to use...
i think it is 1.2A/sq.mm for Aluminium...
550/1.2 = 458 sq.mm Aluminium cable u have to use...
like this.... the current carrying capacity is different
for different materials...
Is This Answer Correct ? | 23 Yes | 5 No |
Answer / dilip singh
Normally if you go with the size of cable in catalogue, you
will observe the if cable is of 400sqmm thenit carries
about 300A current and similarly for other ratings so you
can guess by size of cable selected. but it will not be
correct all the time. may it will vary by some value.
Is This Answer Correct ? | 13 Yes | 5 No |
Answer / u.chandarasekar
It is very vert Hard Question for me i never know the
answer.
In 28 Years exp. first time i face this kind of qus. That's
a main reason BGR Energy Terminate me.
Is This Answer Correct ? | 5 Yes | 1 No |
Answer / s.manikandan
we are know the formula R=Pl/A. P - resistivity of copper or
Aluminium, L - Length of wire,A - Area of wire, and We use
I=V/R formula
Is This Answer Correct ? | 2 Yes | 2 No |
Answer / sk
In copper cable 1sq.mm equals to 4 amps so 150sqmm*4 amps that equals to 600 amps , and we will be in safer side
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / syed masood
t he cable size depends upon the ams rating but the cables size defined standard value the ams rating enclosed this values some values 2.5,4,6,10,......630
first you have to know full conductor size standard value
then you calculate cable size depends upon the ams by using this relation cu=2-5ams per sq.mm
al=1.2-2ams per sq.mm
4 guage for 125-150ams convert guage into mm
from kadayanallur syed masood electrical engineer
national college of engineering
Is This Answer Correct ? | 0 Yes | 2 No |
Answer / amit
u van not get tha exact size of cable widout catalouge
Is This Answer Correct ? | 4 Yes | 9 No |
generally, for low rating full load current should be 3
times for aluminium cable, & 4 times for copper cable.
so, here 550/4=137.5 sq mm,
also 550/3=183.33 sq mm.
but this is for low rating, in high rating ratio is
decrease,
i.e. for copper 550/3= 183.33 sqmm
& for aluminium 550/2= 275 sq mm.
Is This Answer Correct ? | 5 Yes | 11 No |
What is the RME and explain the full form and what is the RME work?
How do you classify the different types of torques?
for star delta connection,,why the contactor star not burn,when red,yellow and blue cable is looping.
2 Answers Mahindra Water Utilities,
how dose servo motor works
If single phase voltage level is 230V than why three phase voltage level is not 660V ?, but it is only 440V.
16 Answers BSNL, DOS, EFS, HMT, L&T, TCS, ThyssenKrupp,
Control wiring of a dol starter for forward and backward
what is the difference b/w neutral and ground?
What are the major reasons for balancing hydro-thermal mix?
which Machine u will prefer to use at place where Flammable gases are coming out & why ??
which types of tests are required after commissioning of 6.6 kva tranformer?
why we still use sinusoidal waveforms for transmission and utilisation (we know generation is sinusoidal), instead of other ac waveforms such as triangle, sawtooth, square etc.,? is there any mathematical derivations to prove sinusoidal is efficient than others?
resistance of transformer oil=?