In three phase energymeter the spindle rotating backward
why?
At least, two current coil connections are reversed.There
are usually 8 terminals in a 3 phase EM. From left, termial
no. 1,3,5 are for main side (incoming) for the 3 phases and
2,4 and 6 are for their load side .7an8 are for neutral and
are shorted inside the meter.This reverse rotation usually
takes place when CTs are used and directions of currents
are reversed.
Is This Answer Correct ? | 0 Yes | 0 No |
Why we are testing cables with dc?
what is plunger and what's the use of it in motor alignment?
What is primary distribution and secondary distribution of ac power?
any one can explain what is the size of pvc,armoured, various sizes of powr cable dia?
why field winding is placed on rotor winding not on stator winding in case of synchronous machine?
How to select the Cable size for 550 Amps Load without seeing the cable Catalogue?
what is "PE" earthing? and what do u know abt 16mm cable?
IN OLTC we observed "OUT OF STEP" Alarm, we have two different transformer, when both are in parallel this type of alarm observed. what's the meaning of this alarm and why it occurs???
what are the stresses in circuit breakers ?
what are lightning masts?what is their purpose???
WE know that for Inductor X=2pifL,In DC f=0,then X=0 so,V=IX=0;But In the DC excitation of rotor of AC generator,DC motor field coil which coils are inductor so why does not applying DC voltage short the rotor coil of AC generator and field coil of motor?If it would then DC source might be damaged but it is not happened. Why does the strand conductor of Electrical power transmission line make twist?