what happens when the profibus fails while in operation
(operation of a valve)?
Answers were Sorted based on User's Feedback
Answer / raj anu raj
the valve will go to its fail safe position ie.. either
open or close
Is This Answer Correct ? | 24 Yes | 1 No |
Answer / varathan
when communication failure occurs, Valve positioner have
three different action depend on application.
1. Fail to close
2. Fail to open
3. Fail to Standstill.(remain in the previous position)
Note: In automatic closed loop system, during failure
condition; controller must be forced back to manual mode
for safe operation
Is This Answer Correct ? | 22 Yes | 1 No |
Answer / vijay singh
if profibus fails in operation.Valve positioner have
different action depend on application.
1.if valve is fail to open then valve will be in fully open
position
2.if valve is fail to close then valve will be in fully
close position.
Is This Answer Correct ? | 8 Yes | 2 No |
Answer / ecxlsync
in an event of profibus failure or an absence of command signal, some valves will remain its current position, some will return to its safe position (fail safe).
There are valves designed to fully close (Fail to Close) or Fully Open (Fail to Open) in an event of failure.
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / jignesh parekh
during fail of profibus a valve be remain as it is. because
there is no command to travel a control valve move close or
open.
Is This Answer Correct ? | 2 Yes | 15 No |
how control valve works?
With N nodes and B branches what will have a network ???
I am a electronics and instrumentation fresher trying for a job in IT sector. what do need to prepare for the interview?
what is the working principle of ABB gas analyser of kiln in cement industries
Please can anybody help for control valve sizing step by step procedure?
what is solenoid valve?
what is the input of ph sensor and meter during the calibration time and what is the output?
Calibration procedure for water rotameters
WHAT IS A SYMPTOM OF FAULT WITH THE SPAN OF AN INSTRUMENT? 1)ZERO-POINT AND 100% ARE CORRECT BUT NOT A MID-RANGE. 2)ZERO-POINT IS CORRECT ,BUT 1005 INPUT IS NOT GIVING 100% OUTPUT. 3)LINEARITY PRBS. 4)1005 O/p IS CORRECT BUT ZEO POINT IS WRONG.
How can you convert an SR Flip-flop to a JK Flip-flop?
How ejector(or)evactor air pump is working in thermal power plant?
what is the difference between impact plate n coriolis type solid flow meters n how they works....n which one is better