what is the difference between ELCB and RCCB
Answers were Sorted based on User's Feedback
Both are same thing Only difference is that RCCb is
technical name and ELCB is commercial name.RCCB is residual
current circuit breaker which works on principle of residual
current and ELCB is earth leakage circuit breaker which also
works on principle of residual current.
Is This Answer Correct ? | 17 Yes | 4 No |
Answer / adhi
ELCB:-An ELCB is a specialised type of latching relay that
has a building's incoming mains power connected through its
switching contacts so that the ELCB disconnects the power
in an earth leakage (unsafe) condition.The ELCB detects
fault currents passing from live (hot) to the earth
(ground) wire within the installation it protects. If
sufficient voltage appears across the ELCB's sense coil, it
will switch off the power, and remain off until manually
reset. An ELCB however, does not sense fault currents
passing from live to any other earthed body.
RCCB:-A residual current device (RCD), or residual current
circuit breaker (RCCB), is an electrical wiring device that
disconnects a circuit whenever it detects that the electric
current is not balanced between the phase ("hot") conductor
and the neutral conductor. Such an imbalance is sometimes
caused by current leakage through the body of a person who
is grounded and accidentally touching the energized part of
the circuit. A lethal shock can result from these
conditions; RCDs are designed to disconnect quickly enough
to mitigate the harm caused by such shocks.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / ashoke
The difference between ELCB and RCCB is that ELCB works on
earth leakage voltage and RCCB works on earth lakage current .
Is This Answer Correct ? | 8 Yes | 6 No |
Answer / godfather
I Agree with Iqbal .Both are current residual control devices and .....vipu RCCB/ELCB do not provide protection against overload the device which provides earth leakage as well as over current protection is called RCBO.
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / vipu p k
elcb is using the protection of earth leakage.but rccb is
using earthleakage protection and over current protection
Is This Answer Correct ? | 4 Yes | 8 No |
If a contactor need to replace with faulty one. what I want to check?
How capacitor connect in 3 phase supply???
An ELHNC 80amp 240v 30mA RCD is tripping periodically, every 30 - 180 seconds is it safe to disconnect the protection circuit?
What happens if there is no nuetral in the power system?
what is diffence between synchronus and asynchronus AC motor.?
what is the resistence of human body?
what do u mean by knee point voltage?
I have a 25 KVar capacitor bank at my facility.How to check the capacitor bank ??
WHAT IS A BASIC DIFFERENCE BETWEEN THYRISTOR,TRIAC AND A DIAC.AND WHAT R THERE APPLICATIONS?
why do we need the body earth?
how to test reverse power trip?
what are the main problems that happen in an emergency light and how to fix them ?