if we convert kw into Ampers,which one formula use by
us,pls tell me?
Answers were Sorted based on User's Feedback
Answer / sandip
In Dc supply we just divide by voltage and in AC supply we
divide with voltage and Power Factor depending upon non-
linear load
| Is This Answer Correct ? | 20 Yes | 4 No |
Answer / k.jagadeesh
In DC supply. kw/voltege
In AC supply (3ph)= kw/ 1.732xVxPFX Efficiency
In AC supply (1PH) kw/v
| Is This Answer Correct ? | 15 Yes | 3 No |
Answer / sameer
First covert kw to kVa kva = Kw / PF(0.8)
Rated full load current in A = (Total connected load in
kva / sq.rt * 3 x Supply Voltage) x 1000
| Is This Answer Correct ? | 8 Yes | 0 No |
Answer / jaimin
FOR 3 PHASE CKT
KW=ROOT(3)*V*A POWER FACTOR
A=KW/(ROOT(3)*V*POWER FACTOR)
FOR SINGLE PHASE CKT.
KW=V*A*POWER FACTOR
A=KW/V*POWER FACTOR
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / harish
KW is always a real quantity and hence we do not
require any power factor term...simply divide he given kw
by the voltage and you get the required amperes...
| Is This Answer Correct ? | 14 Yes | 20 No |
Answer / riyadh
we know load watts , u apply below formula for 3 phase &
single phase
3 phase I = Total load in watts/3*220V
1 phase I = Total load in watts/220V
| Is This Answer Correct ? | 3 Yes | 11 No |
single phase power supply give to separate one steel coup with water, what reaction create
difference between Ac and Dc mcb ????
HOW TO CALCULATE UPS BATTERY BACKUP TIME
What is the exact load current needed for a place which has 100nos of bulb of each 100w?
how terminal voltage increases when load is capacitive (leading pf load)? (explain practically what is happening, not using phasor diagram
explain Uninterrupted power supply detailed electronical operation with circuit diagram
What is the difference between voltages or potential difference? And what are they?
Wat wil happen if Transformer is operated at 100 HZ Frequency?
On a transformer name plate %IZ(%Impedence) is mentioned. What is the meaning of %IZ and how it is calculated?
3 Answers Ambe Consultancy, Siemens,
What is the maximum load an electric engine can pull??
Distribution transformer we provided 2 separate earthing pit for Body and 2 separate earthing pit for neutral,we can not connect separate body earthing pit to other earthing pit but we do metal glanding in secondary side cable termination in both side, transformer and PCC panel (LT Panel), is this safe for transformer and other equipment?
Stator of 3-phase IM has 3 slots per pole per phase, calculate number of stator pole pairs. A 1 B 6 C 2 D 3
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)