Answer / jaykaran gadhvi
the answer is
line current =kva( 3 phase) / (sqrt(3)* line voltage in kv)
so
kva ( 3 phase) = sqrt(3)* line voltage in kv * ampere
| Is This Answer Correct ? | 15 Yes | 0 No |
Answer / joseph
You can use the basic formula:
VA = [Voltage X 1.732] * Current
or
VA = [Voltage * 1.732] * I
Hence, VA of a 3 Phase system with 1500A Current current at
440V will be:
VA = [440 * 1.732] * 1500
= 1143120 VA or 1143 KVA.
| Is This Answer Correct ? | 12 Yes | 2 No |
Answer / v.chandrasekharreddy
Amps when
kVA is known ,I=KVA*1000/[1.732*VOLTAGE]IN THREE PHASE
Amps when
kVA is known
I=kVA x 1000/VOLTAGE SINGLE PHASE
| Is This Answer Correct ? | 10 Yes | 6 No |
Answer / yogesh raste
In order to convert amperes to KVA multiply supply voltage
(V) with current(I).
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / p.baskar
Amps =KVA*1000/[1.732*VOLTAGE]IN THREE PHASE
Amps =kVA x 1000/VOLTAGE SINGLE PHASE
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / thebalu007
kw = Route that mean 1.732*v*i*cosPai
I = route that mean 1.732*V
because kva does not having power factor that men cos pai
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / dinesh jakhar
Apparent power =V.A
Unit of apparent power is VA or KVA or MVA
So if you want to find KVA simple formula u just need voltage and current
kVA= KV(voltage) * A (current)
| Is This Answer Correct ? | 0 Yes | 0 No |
MCB Rating
what effect on electrical equipment if PF is gone over 0.996 in leading when provider say that its keep in minimum 0.996lagging
one KVAR takes how much amps, and how to add power capacitors to electrical panels, for example if one of the MCC drawn 800amps means how much KVAR required
What do you meant by soft start?
IS RTCC AND OLTC REQUIRED FOR 500 KVA 11KV/433V TRANSFORMER FOR AN INDUSTRY?
7 Answers IGCAR, TNEB Tamil Nadu Electricity Board,
What is polar plot?
why DG,Transformer,UPS capacity will be tell in KVA but not in KW?
What is different between DOL(Direct on line starter), VSD, S/S(Soft starter), and A/T(Auto Transformer)
i am confused about generator. i have generator of 380 KVA that is 304 KW by that formula KW=KVA*0.8... then by this formula I=KW/V*1.732*0.8 the amperes are 528.673. so that is the load which i put on one phase of generator or this is total 3 phase load on Generator.......
what is the EMF
Transformers with dc supply
where we sense the fault from the transmission lines?any operation example for distance relay?rear panel connection for this relay?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)