if we convert Ampers into kva,which one formula use by
us,pls tell me?
Answers were Sorted based on User's Feedback
Answer / jaykaran gadhvi
the answer is
line current =kva( 3 phase) / (sqrt(3)* line voltage in kv)
so
kva ( 3 phase) = sqrt(3)* line voltage in kv * ampere
| Is This Answer Correct ? | 15 Yes | 0 No |
Answer / joseph
You can use the basic formula:
VA = [Voltage X 1.732] * Current
or
VA = [Voltage * 1.732] * I
Hence, VA of a 3 Phase system with 1500A Current current at
440V will be:
VA = [440 * 1.732] * 1500
= 1143120 VA or 1143 KVA.
| Is This Answer Correct ? | 12 Yes | 2 No |
Answer / v.chandrasekharreddy
Amps when
kVA is known ,I=KVA*1000/[1.732*VOLTAGE]IN THREE PHASE
Amps when
kVA is known
I=kVA x 1000/VOLTAGE SINGLE PHASE
| Is This Answer Correct ? | 10 Yes | 6 No |
Answer / yogesh raste
In order to convert amperes to KVA multiply supply voltage
(V) with current(I).
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / p.baskar
Amps =KVA*1000/[1.732*VOLTAGE]IN THREE PHASE
Amps =kVA x 1000/VOLTAGE SINGLE PHASE
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / thebalu007
kw = Route that mean 1.732*v*i*cosPai
I = route that mean 1.732*V
because kva does not having power factor that men cos pai
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / dinesh jakhar
Apparent power =V.A
Unit of apparent power is VA or KVA or MVA
So if you want to find KVA simple formula u just need voltage and current
kVA= KV(voltage) * A (current)
| Is This Answer Correct ? | 0 Yes | 0 No |
in alternator why on load terminal voltage is less than no load teprminal voltage
Sir, plz tell me the relation b/w KW and frequency in Variable frequency Drive?
what is the prosses for getting of 33kv licence (i have completed my engineering degree & working in 33kv substation for contract basis )????
How to Calculate Contracted Maximum demand using motor Hp or Current
What is Goerges phenomina to start SYCHNOUSMOTOR?
what is the difference between KVAR & KVA ?
11 Answers Bombay Rayon Fashions, Hyundai, Pricol,
What is different between Metering CTs and Protection CTs?
WHAT SHOULD BE THE RATING OF generator required to run a pump motor of 45 Kw.
As per the Anchor capstan motor specification, full load current is 200A. starting current is 1750 A and acceleration time is less than 8 seconds. Please guide for selection of cable size.
explain about RTCC
What will be result if we connect LT votage to the terminal of HT motor?
how the 3phase induction motor is running in 2phase supply with help of capacitor?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)