how much insulation resistance 11kv & 33kv under ground
cable between earth to phase & phase to phase.
Answers were Sorted based on User's Feedback
Answer / vinay gupta
between earth to phase it must be from 50megaohm to
infinite. and from phase to phase it must be from
500megaohm to infinite.
| Is This Answer Correct ? | 50 Yes | 13 No |
Answer / praful
Thumb rule to measure the IR value is add 1.5 to the
operating voltage (convert the voltage in KVolts) the
answer is the min. required safe IR value (Mega ohm).
For Example the Operating voltage is 22kV then 1.5 + 22 =
23.5. 23.5 Mega Ohm is the min. IR value required.
The IR value must alaways be on higher side.
| Is This Answer Correct ? | 28 Yes | 11 No |
Answer / shivkumar sharma
Between Earth to phase insulation resistance must be twice
of operating voltage by H.T.( 2.5 k.v./5 k.v. )megger
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / mintu kumar pandit
insulation resistance 11kv to 33kv minimum IR value for new
cable ph to ph & ph to earth 400 megohms for 100 meter 1 minitue
cable after repair the resistance must not be less that
10 megohms ( megger size 1kv )
| Is This Answer Correct ? | 3 Yes | 1 No |
wat system call?
What is the difference between DOL starter and star delta starter
How does frequency affect KVA rating of a transformer? If a 500 kva, 400 v, 60 hz t/f is to be operated on 50 hz frequency then how will its KVA rating change? a-increase b-decrease c-remains same Also explain why do u think like that.
What is meant by time harmonics and space harmonics?
The efficiency of a 100kva transformer is 0.98 at full load as well as half load , for this transformer what is the Copper loss at full load ?
how to interlock 2 incomer,1 buscoupler MCCB,like we interlock an ACB... pls answer this question and if possible send me the ckt diagram..
What is the transformenr turns ratio.
what is the diffrent between ups and inverter
What is the difference between class0.1 and class 0.1s accuracy of current transformers
can we calculate the diameter of the cable by its cross section?
What is the gross weight to copper ratio in slip ring induction motor of 4000 HP,6.6 kv, 372amp, 992 rpm GE motor.
What will be the size of copper cable (each for 3 phase and 1 neutral) from Service connection Kit-Kat to Panel Board (i.e. to main switch) for a 6 pole 3-phase AC induction motor of 200 H.P. capacity? Amp-255 A, Frequency:- 1450 rpm.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)