how to calculate the neautral earthing conductor size for a
500kva dg set.
Answers were Sorted based on User's Feedback
Answer / krl raju
If alternator voltage is considered 415 V, then rated
current of the Alternator is
=500*1000/(1.732*415)=695.6Amps.
Hence we need to select the neutral conductor to withstand
the half of the full load current i.e 350Amps
Is This Answer Correct ? | 9 Yes | 2 No |
Answer / sakthivel
hi mr krl raju sir i want which size of contuctor you
chuse about 350 amp neutral earth comtuctor give full
details
Is This Answer Correct ? | 2 Yes | 0 No |