How do you select a cable size(cu&Al)for a particular load?
Answers were Sorted based on User's Feedback
Answer / sreenu
Based on KW/HP value the current rating can be caluculated
and based on current rating of Mains & cable size can be
caluculated.
for example.
HP of the motor is :A HP
KW of load is :A HP/735.5*Efficiency(E).
Generally eddicieny of the motor can be asuumed 0.8 to 0.9
Current(C) is :A HP/735.5*E*(1.73*V* cosQ)
Cos Q generally asumed as 0.8 to 0.9
If the value of current is C, the current capacity of cable
reuired is Appx. 1.5*C.
Based on cable catalogue provided by the cable manufacturer
the size of the cable can be selected.
For eample. If you use al. cable, the size of cable is
bigger than copper cable.
Rating of mains: 1.5* C, but fuse arting is C only.
Is This Answer Correct ? | 3 Yes | 1 No |
what is the installation process for lifts
why generator and t/f ratings given in kva?
if we want to increase the back up time of an UPS what should we do ? if we want to decrease the charging time of a battery/batteries attached with the UPS what should we do ?
how to calculate the cable size
Using 11000V/433V,3 ph,50Hz,500 KVA, what is the maximum capacity of motor in KW that can be connected and started at a single moment? Also explain about any calculations and formulas used in deriving the same.
To make a basic instrumentation amplifier, it takes A One op-amp with a certain feedback arrangement B Two op-amp and seven resistors C Three op-amps and seven capacitors D Three op-amps and seven resistors
circuit diagram of ht panel
What is the actual formula for transformer short circuit test? below i given rating of the transformer.. 1000KVA, pri 11KV, Pri amp 56A. %Z 5.95..
what is balanced beam relay
Either the Armoured Earthing strip of HT 3 core cable have to pass through CB CT or not , why ???
WHY DO VOLTAGE TRANSFORMERS FAIL DURING EARTH FAULT IN THE DELTA CONNECTED 6.6KV ELECTRICAL SYSTEM
What is the working principle of ceiling fan?