Using 11000V/433V,3 ph,50Hz,500 KVA, what is the maximum
capacity of motor in KW that can be connected and started at
a single moment? Also explain about any calculations and
formulas used in deriving the same.
Answers were Sorted based on User's Feedback
Answer / amr hamad
the transformer should not be full loaded all the time so,
its maximum load should be .8 of its full load rating =400kva
so , maximum power of motor should not increase 320kw with
0.8 pf
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / dinesh kannan
Since the motor is connected in 433V side , we consider
powerfactor 0.8.so maximum connected capacity of motor is
500*0.8, but we have to run the motor in single start
there are so many methods are there to start the motor like
DOL, star delta starters based on the starter and starting
current of motor we deside the maimun rating of motor( to
start the motor, minimum 70% of voltage is required
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / vijay krishna rao
considering DOL type of starter (so starting time will be
appx 6 times the rated current)and also considering starting
time of motor may affect the Xmer, then 500/6=83.33 MVA.
Motor rating (pf=0.8)=83.33*0.8=66.66kW (efficiency=100%)
If soft starter is used then motor rating can go upto Xmer
rating.
| Is This Answer Correct ? | 0 Yes | 1 No |
why is the number of turns different in current and potential coils of wattmeter..?
Different types of relay fault which phase sequence??
What is the differentional relay...what is the work of this in power Tx. how it is works..
How can I calculate the Mega watts required to run a plant having many electric motors and other electrical components.
In 3phase power= Root*3*v*i*cos@ What is the power in 2phase....??? and Derive it
3,12,24,33,_ ,75,150 Find the missed number in this sequence
control wiring purpose,standards, ferrule code standard, interlock, schematic, symbol
why the generating voltage in India is 11kV or why is it be transmitted as multiples of 11
34 Answers ACC, Bhel, ECI Engineering and Construction, NTPC, SBL, Senthur Power Services,
can we replace d.c.motor by 3 phase induction motor for a particular application
why nearly all the voltage levels are in the multiples of 11 like 3.3 ,6.6 ,33 ,11 kv.....
what is PPI DB?
2 Answers Priyanka Electricals,
how can we change the phase angle b/w two phase?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)