Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


generaly all power generating devices is expressed in KVA
or MVA then why power ststion is expressed in MW

Answers were Sorted based on User's Feedback



generaly all power generating devices is expressed in KVA or MVA then why power ststion is express..

Answer / anubis

KVA or MVA is used to measure apparent power. MW is used
for real power. Since the resistance and reactance for a
generating device is known, the apparent power can be
calculated. For the power station the apparent power will
not only depend upon the internal impedence of the station,
and the wies, but also upon the grid. This is not a fixed
number and varies with conditions, thus making it
impossible to judge. Thus it is safer to just give the real
power and then calculate th apparent power depending upon
the load used.

Is This Answer Correct ?    16 Yes 1 No

generaly all power generating devices is expressed in KVA or MVA then why power ststion is express..

Answer / b.prakash.

KVA meanas apparent power it depends on power factor if
power factor is high the efficiency of system also high.
But in MW it true power means (load) if u r using a 2kw
heater then it will consume 2 kw. but in KVA suppose for ex.
transformer capacity is 1000kva & PF is 0.8 means we can
use only 80% of the total kva & it depends on the load also
that which type of load u r using. if u r using, capacitive
load or resistance load then the PF will be high. But if u
r using Inductive load then the PF will be less.

Is This Answer Correct ?    6 Yes 1 No

generaly all power generating devices is expressed in KVA or MVA then why power ststion is express..

Answer / nikunj thakkar

the basic reason behind this question is that all the power station are heaving there reactive and active power delivering capacity so they are specifying that maximum power that can be delivered by company is in MW

Is This Answer Correct ?    2 Yes 0 No

generaly all power generating devices is expressed in KVA or MVA then why power ststion is express..

Answer / kishore

IT IS BECOZ POWER STATION RATING INCLUDES
EFFICIENCY/RATING OF ALTERNATOR AS WELL AS TURBINE.

Is This Answer Correct ?    5 Yes 6 No

generaly all power generating devices is expressed in KVA or MVA then why power ststion is express..

Answer / jeet

Generally our devices losses only depends on voltage and current it does not includes P.f so we take there ratings in MVA or KVA but in power house the power generated and transmitted is depends on P.f also along with V and I.Therefore we keep rating of power house in Kw and aplliences in KVA or MVA.

Is This Answer Correct ?    0 Yes 1 No

generaly all power generating devices is expressed in KVA or MVA then why power ststion is express..

Answer / ynrao

Along with MW the rated PF also given on name plate of Gen
to display the optimum loading. That means at that PF the
rating is __ MW.

Is This Answer Correct ?    1 Yes 4 No

Post New Answer

More Electrical Engineering Interview Questions

we want install 11KV generator to supply power 12km far from the power house.Load to be fed is 1MW.which conductor should we use and wat will be transmission line losses?

1 Answers   CEM Engineering,


What is the difference between lubricating oil and insulating Oil?

4 Answers   Orchid,


what is per unit impedance?

3 Answers  


the resstance of a thermistor is 5000 ohm at 25degreeC and coefficient is .04/degCel. A measurement with lead resitance of 10 ohm will cause an error of

1 Answers   GATE,


define the non synchoronism of synchoronous machine in general g or m??

0 Answers  


ASTM D 3455 - Standard Test Methods for Compatibility of Construction Material with Electrical Insulating Oil of Petroleum Origin has been used for Testing Transformer Oils with a product placed in it. Aged Control Oil has a Power Factor of 0.032% at 100°C. Aged Oil with a Test component has a Power Factor of 0.093% at 100°. Is this increase acceptable? If not why? How much increase is acceptable?

0 Answers  


How does frequency affect KVA rating of a transformer? If a 500 kva, 400 v, 60 hz t/f is to be operated on 50 hz frequency then how will its KVA rating change? a-increase b-decrease c-remains same Also explain why do u think like that.

8 Answers  


Explain in details how you would react to an unexpected incident when your supervisor or manager is not around to give instructions?

1 Answers  


why is corona loss greater in a stranded conductor as compared to a solid conductor ?

2 Answers  


we have earthmat at 110KV substation.we would like to take earth resistance.b some says that by connecting earth megger terminals (C1,P1) at middile point of earthmat (at riser) will cause voltage gradient at other earthmat nods and dont get exat earth resistance.when connecting at end nods will get exat value . is it correct .please explain

0 Answers   TNEB Tamil Nadu Electricity Board,


why insulators are colured in brown only?

3 Answers   Transco,


what are the compensations considered while designing a transmmision line.

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)