generaly all power generating devices is expressed in KVA
or MVA then why power ststion is expressed in MW
Answers were Sorted based on User's Feedback
Answer / anubis
KVA or MVA is used to measure apparent power. MW is used
for real power. Since the resistance and reactance for a
generating device is known, the apparent power can be
calculated. For the power station the apparent power will
not only depend upon the internal impedence of the station,
and the wies, but also upon the grid. This is not a fixed
number and varies with conditions, thus making it
impossible to judge. Thus it is safer to just give the real
power and then calculate th apparent power depending upon
the load used.
| Is This Answer Correct ? | 16 Yes | 1 No |
Answer / b.prakash.
KVA meanas apparent power it depends on power factor if
power factor is high the efficiency of system also high.
But in MW it true power means (load) if u r using a 2kw
heater then it will consume 2 kw. but in KVA suppose for ex.
transformer capacity is 1000kva & PF is 0.8 means we can
use only 80% of the total kva & it depends on the load also
that which type of load u r using. if u r using, capacitive
load or resistance load then the PF will be high. But if u
r using Inductive load then the PF will be less.
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / nikunj thakkar
the basic reason behind this question is that all the power station are heaving there reactive and active power delivering capacity so they are specifying that maximum power that can be delivered by company is in MW
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / kishore
IT IS BECOZ POWER STATION RATING INCLUDES
EFFICIENCY/RATING OF ALTERNATOR AS WELL AS TURBINE.
| Is This Answer Correct ? | 5 Yes | 6 No |
Answer / jeet
Generally our devices losses only depends on voltage and current it does not includes P.f so we take there ratings in MVA or KVA but in power house the power generated and transmitted is depends on P.f also along with V and I.Therefore we keep rating of power house in Kw and aplliences in KVA or MVA.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / ynrao
Along with MW the rated PF also given on name plate of Gen
to display the optimum loading. That means at that PF the
rating is __ MW.
| Is This Answer Correct ? | 1 Yes | 4 No |
what is the difference between neutral
what is the full Form of AAC ant conductor?
At 765Kv, I have seen the use of PT at line side for metering and CVT for protection, although as far as my knowledge is concern, PT at this voltage level will have huge loss and more cost as compared to CVT as CVT can also perform same function of Protection and Metering? So my question is why use PT and not CVT for metering and protection in order to reduce the cost.
On what basis no of earth pits are to be decided either for transformers or for equipment?
why insulators colour is BROWN?
my motor rating is 800HP, 128Amps, 3.3kV. What is capaitor bank i can use for PF improvement to 0.990?
After synchronizing the running generator with grid, the avr getting tripped and the generator breaker also oettong tripped, before tripping the avr the pf meter of generator is showing leading pf please kindly give a suggestion to rectify this problem.
What is the Different Between Breaker and One and half breaker.
What is the difference between an ELCB and a RCD?
Sir Power transformer :- (in generating station) Alternator terminals side - Delta HT transmission line side - Star Why?
What is WLD System????
3 Answers Emerson, HCL, Honeywell, Tata Communications,
What is ahu ? Working principal.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)