generaly all power generating devices is expressed in KVA
or MVA then why power ststion is expressed in MW
Answers were Sorted based on User's Feedback
Answer / anubis
KVA or MVA is used to measure apparent power. MW is used
for real power. Since the resistance and reactance for a
generating device is known, the apparent power can be
calculated. For the power station the apparent power will
not only depend upon the internal impedence of the station,
and the wies, but also upon the grid. This is not a fixed
number and varies with conditions, thus making it
impossible to judge. Thus it is safer to just give the real
power and then calculate th apparent power depending upon
the load used.
Is This Answer Correct ? | 16 Yes | 1 No |
Answer / b.prakash.
KVA meanas apparent power it depends on power factor if
power factor is high the efficiency of system also high.
But in MW it true power means (load) if u r using a 2kw
heater then it will consume 2 kw. but in KVA suppose for ex.
transformer capacity is 1000kva & PF is 0.8 means we can
use only 80% of the total kva & it depends on the load also
that which type of load u r using. if u r using, capacitive
load or resistance load then the PF will be high. But if u
r using Inductive load then the PF will be less.
Is This Answer Correct ? | 6 Yes | 1 No |
Answer / nikunj thakkar
the basic reason behind this question is that all the power station are heaving there reactive and active power delivering capacity so they are specifying that maximum power that can be delivered by company is in MW
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / kishore
IT IS BECOZ POWER STATION RATING INCLUDES
EFFICIENCY/RATING OF ALTERNATOR AS WELL AS TURBINE.
Is This Answer Correct ? | 5 Yes | 6 No |
Answer / jeet
Generally our devices losses only depends on voltage and current it does not includes P.f so we take there ratings in MVA or KVA but in power house the power generated and transmitted is depends on P.f also along with V and I.Therefore we keep rating of power house in Kw and aplliences in KVA or MVA.
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / ynrao
Along with MW the rated PF also given on name plate of Gen
to display the optimum loading. That means at that PF the
rating is __ MW.
Is This Answer Correct ? | 1 Yes | 4 No |
what is negative d.c. voltage, why this voltage is used in base transciever station.
What are capacitive,resistive,inductive surge absorbation? What is ferranti surge absorber? What is lagrangian cost? What is Px operator?
what type of relay has to be used for tripping the circuit from mains when a fault occur in a machine
What is derating?, Why it is necessary, it is same for all means for drives, motors,and cables.
what is the use of power transformer in GSS.
0 Answers College School Exams Tests, DLF, TCS,
Why don't we use ground free electricity to avoid electric shock.As birds are do not get shock.
Explain the operation of variable frequency transformer?
EHV current carrying parts need to have smooth finish,then how can a 245kv GIS with emery finish can run so long?
why we take movement of rotor always in counter-clockwise direction in 3-phase induction motors?
Operation carried out in thermal power stations?
What is the meaning of high reputuring in HRC fuse.?
How much depth n width required for laying of 1X70 Sqmm Cable in Desert???
0 Answers Alka Electromech, Aramco,