if generator is running in iso mode parrallel with grid and
suddenly grid breaker off what will happen?
Answers were Sorted based on User's Feedback
Answer / blake australia
If generator is running in ISOC mode (opposed to base
loading) and the grid connection is lost the generator will
try to pick up the load on the connected network. If the
load is too big then the generator will trip. If the load
isn't the generator will continue to run as before. ISOC
mode means that the generator is running in its own
frequency control, so if it looses the grid frequency it
can still run based on its own frequency.
If the generator was running in base load and the breaker
trips the generator will have no frequency reference.
Usually they are configured to change themselves back into
isoc when grid reference is lost but you should check if
unsure.
| Is This Answer Correct ? | 17 Yes | 1 No |
Answer / vincent omwikha
depending with load supplied, the generator will continue
running if it can sustain the load, but it will trip
immediately if the load is to big for it
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / pg
Generator can not run in Iso Syn mode while running
parralel with Grid.
If it is runnin parallel with grig in Iso Syn mode it will
trip in Overload or reverse power.Because in iso mode
Generator run at constant frequency and grid frequency vary
so it may overload or trip on reverse power.
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / mahmud
many reasons-
1.ROCOF settings.
2.O/U voltage
3. O/U Frequency
etc.
| Is This Answer Correct ? | 2 Yes | 2 No |
if we give connection of 100watts bulb through a single phase energy meter ,the disc of a meter rotates why it happens?
What is the meaning of key single line diagram?
Advantage of 11KV ring main system with open point
1 Answers Alam Group of Companies,
how much amps can i connect for 4core 120mm armade cable
How to calculate of maximum demand if given 628kw, 785kva, 0.8 p.f.
star delta advantage and disadvantage?
sir, what is the importance of Fault MVA. how to calculate fault mva of 33kv substation connected by 6.5 km line(single circuit with equal spacing) with 110/11kv transformer in 110kv susbstation.the fault mva on 11 kv bus in 110kv susbstation is 208mva.
EXPLAIN THE ESSENTIAL FACTORS WHICH INFLUENCES THE CHOICE OF SITE FOR A HYDRO ELECTRIC POWER PLANT
what is motor
how to calculate cable size, olr rating, contactor rating and mccb rating,to below given details three phase motor 75 kw,415 v,.85 pf,50 hz?
what is role of mpu in dg
I want to know that a 160kva diesel generator contains capacity of 160kva on each phase like R=160 Y=160 B=160 total RYB=480kva or it is total capacity of all there phases like RYB=160kva ... thanks in advance ...
2 Answers jlpl, JP Saraswat Engineers,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)