Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


if generator is running in iso mode parrallel with grid and
suddenly grid breaker off what will happen?

Answers were Sorted based on User's Feedback



if generator is running in iso mode parrallel with grid and suddenly grid breaker off what will ha..

Answer / blake australia

If generator is running in ISOC mode (opposed to base
loading) and the grid connection is lost the generator will
try to pick up the load on the connected network. If the
load is too big then the generator will trip. If the load
isn't the generator will continue to run as before. ISOC
mode means that the generator is running in its own
frequency control, so if it looses the grid frequency it
can still run based on its own frequency.

If the generator was running in base load and the breaker
trips the generator will have no frequency reference.
Usually they are configured to change themselves back into
isoc when grid reference is lost but you should check if
unsure.

Is This Answer Correct ?    17 Yes 1 No

if generator is running in iso mode parrallel with grid and suddenly grid breaker off what will ha..

Answer / vincent omwikha

depending with load supplied, the generator will continue
running if it can sustain the load, but it will trip
immediately if the load is to big for it

Is This Answer Correct ?    5 Yes 1 No

if generator is running in iso mode parrallel with grid and suddenly grid breaker off what will ha..

Answer / mahmud

black out may happen.

Is This Answer Correct ?    7 Yes 4 No

if generator is running in iso mode parrallel with grid and suddenly grid breaker off what will ha..

Answer / anil

why?

Is This Answer Correct ?    2 Yes 1 No

if generator is running in iso mode parrallel with grid and suddenly grid breaker off what will ha..

Answer / pg

Generator can not run in Iso Syn mode while running
parralel with Grid.
If it is runnin parallel with grig in Iso Syn mode it will
trip in Overload or reverse power.Because in iso mode
Generator run at constant frequency and grid frequency vary
so it may overload or trip on reverse power.

Is This Answer Correct ?    3 Yes 2 No

if generator is running in iso mode parrallel with grid and suddenly grid breaker off what will ha..

Answer / mahmud

many reasons-
1.ROCOF settings.
2.O/U voltage
3. O/U Frequency
etc.

Is This Answer Correct ?    2 Yes 2 No

Post New Answer

More Electrical Engineering Interview Questions

How many earthings are required for commissioning the Transformer?

14 Answers   Dalmia Group, HSL,


what is kondo syatem in eletrical traction

0 Answers   APCPDCL,


if we know Fault level say 25 KA , How to decide busbar size for Distribution network of 1000 Amp Breaker ? Sample Calculation or Farmula Available or not ?

4 Answers   TCS,


what is the major difference between LIBBP & HIBBP.. which one is most preferable..

0 Answers   ABB,


the power loss in an overloaded line is mainly due to? a. resistance b. capacitance d. inductance d. none

4 Answers  


If cvt is most advance & effective(economically & stability)so why not use instead of VT(11 kv & 33 kv)?

3 Answers  


Capacity of circuit breakers all types

1 Answers   Megatron Solutions,


Why does the Solid state Rectifiers for 3-ph brake motors sometimes have 2 & sometimes 3 output terminals?

0 Answers  


dear friends, how to calculate "Gage" in copper wire , aluminum wire etc. have any formula?

1 Answers  


As per standard, transformer body earthing and other Equipment earthing (Equipment earthing) did not connect. but in LT side termination we are doing metal glanding in both side Transformer to PCC Panel through armoured cable, now X'mer body earthing and PCC Pane earthing (Equipment earthing) both are connect.is this safe for X'mer or other equipment?

0 Answers  


what are the main faults that occur in stabilizers? How they corrected and resolved ? Types of stabilizers ?

0 Answers  


what is the Knee point Voltage?

3 Answers   AAPT,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)