if generator is running in iso mode parrallel with grid and
suddenly grid breaker off what will happen?
Answers were Sorted based on User's Feedback
Answer / blake australia
If generator is running in ISOC mode (opposed to base
loading) and the grid connection is lost the generator will
try to pick up the load on the connected network. If the
load is too big then the generator will trip. If the load
isn't the generator will continue to run as before. ISOC
mode means that the generator is running in its own
frequency control, so if it looses the grid frequency it
can still run based on its own frequency.
If the generator was running in base load and the breaker
trips the generator will have no frequency reference.
Usually they are configured to change themselves back into
isoc when grid reference is lost but you should check if
unsure.
Is This Answer Correct ? | 17 Yes | 1 No |
Answer / vincent omwikha
depending with load supplied, the generator will continue
running if it can sustain the load, but it will trip
immediately if the load is to big for it
Is This Answer Correct ? | 5 Yes | 1 No |
Answer / pg
Generator can not run in Iso Syn mode while running
parralel with Grid.
If it is runnin parallel with grig in Iso Syn mode it will
trip in Overload or reverse power.Because in iso mode
Generator run at constant frequency and grid frequency vary
so it may overload or trip on reverse power.
Is This Answer Correct ? | 3 Yes | 2 No |
Answer / mahmud
many reasons-
1.ROCOF settings.
2.O/U voltage
3. O/U Frequency
etc.
Is This Answer Correct ? | 2 Yes | 2 No |
what is meant by twilight switches 7 where its applicable ?
Why transmission line carryiny high voltage and low current?
3 Answers apspdcl, Universal Power Controls,
what does kirlosker deals with?
What are the criteria shall be considers for sizing Fuse and MCB? If the rated current is 10Amps what should be the fuse size / MCB Size?
hi i wonder will the speed of a 50hz AC motor reduce if i supply it with 25hz?
Why Neutral Busbar CT & transformer neutral CT connected with phase CT in Restricted Earth Fault?
at what rate the micro controller increment its timer....is it 1micro seconds or 1/(12*10^6) seconds
hey guys i scored 910 on GRE and 67 on TOEFL respectively.I have an aggregate of about 74%in my B tech.For which colleges should i apply for an MS program in electrical engineering.I am looking for colleges in NJ,SC,NC,GEORGIA, NY. Please reply with a good response.....
We are installing a 1.6 MVA transformer at our crusher plant and the feeder of HPSEBL is 2 km away at substaion . and a VCB is installed in the substaion which is 2 km away from transformer so we need another VCB near the transformer.
If we have 15000kw connected load in a factory than how much power demand sanction should be taken from electricity board. Pls provide complete calculation.
SAY CORRECT DEFINITION... WHAT IS EDDY CURRENT LOSS? WHAT IS HYSTERESIS LOSS?
What is the unit of inertia constant of rotating machines? Which has more inertia constant between turboalternator and hydroaltermanor and why?