how to caluculate APFC panel rating, my running Load is
1320KW, Present P.F 0.76 to 0.8 we need 0.98 p.f
Answers were Sorted based on User's Feedback
Answer / maprayil
KVAr is square root of (KVA2-kW2). In your case the system KVAr at P.F. 0.76 lag is 1129 KVAr; and P.F. 0.80, it is 990 KVAr. (These are the KVAr values required to take your system P.F. to Unity or 1.00). Please note the following values:-
With a running load of 1320 kW, the Maximum Demand (KVA) of your system at 0.76 PF is 1737 KVA; and at P.F. 0.80, it is 1650 KVA. At a P.F. of 0.98, the Max Demand would be 1347 KVA (KVA = kW/P.F.).
Now that you have the system KVAR & KVA values, the simplest way is to calculate the system KVAR after P.F. is improved to 0.98 lag (your desired value). This can be worked by (considering initial P.F. 0.76):-
KVAR = Square root ((KVA+kW)*(KVA-kW))
= Square root ((1347+1320)*(1347-1320)
= Square root (2667 * 27) = SQRT 72009
= 268 KVAr.
So KVAR required for improving the P.F. of 1320 kW running load from 0.76 to 0.98 is 1129 KVAR (initial system KVAR) minus 268 KVAr (final system KVAR), i.e., 861 KVAr. This KVAR needs to be installed in multiple steps with automatic switching arrangement.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / manish mangla
Actually it is very simple.You know the present pf and
desired pf too.so you can use the formula:
Kvar=kwh(tan(inverse)phi1-tan(inverse)phi2)
Phi1=actual or present pf
Phi2=desired pf
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / s. k. mishra
KVAR^2 = KVA^2 - KW^2 = KVA^2 - KVA^2 * pf^2= KVA^2(1-pf^2)
THEREFORE KVAR= KVA [(1-pf^2)]^1/2
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / tajinder singh
kw=1320
present PF = 0.76
kva =1320/0.76
=1737
for unity pf u require capacitors Panel =1129 kVAr
for 0.98 pf u require capacitors panel =858 kVAr
| Is This Answer Correct ? | 2 Yes | 4 No |
Answer / vijay
Kvar=KVA(1-P.F)
KVA=KW/P.F
Kvar=Kw(1-P.F)/P.F
=1320(1-0.98)/0.98
=250
| Is This Answer Correct ? | 20 Yes | 33 No |
Answer / cibi
by using delsigma relations or fiuys charts apf panel rating
could be determined
| Is This Answer Correct ? | 18 Yes | 36 No |
what is the magnetic (electric) center)
WHICH ONE IS PREFERRED, VERTICAL OR HORIZONTAL PUMP WITH COMPLETE TECHNICAL DETAILS
What is the purpose of gravity tank in the stern tube
An employ has after increment has Gross Salary 22000 rupees per month. Earlier he was covered in ESI . now should we deduct ESI from his salary or not.
Which heating value is indicated by a calorimeter and why ?
why with the increase of pressure latent heat of steam decreases?
Whether superheated steam can be treated like ideal gas ?
What is max pressure?
WHAT IS MEAN BY DENSITY COMPESATIVE STEAM FLOW EXPLANE?
what is the responsibility of assistant manager in welding in goa shipyrad company?
Identify the parts of steam turbine
0 Answers ABC Inc, RRB, Siemens,
What is the selection criteria of Natural Draught Cooling Tower and Induced Draught Cooling Tower . Where we prefer NDCT and where IDCT.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)