Answer Posted / suresh
VFD – variable frequency drive..
VFD is useful in energy saving because it reduces the
motor speed as demand decreases.When the speed is reduced
the power consumption Will also reduce because ,
Power = (speed)3 {cube of speed}
For example if the speed is reduced to 80% of the maximum
value the power consumed will be reduced by 50%
Power consumed = (0.8)3 = 0.512 = 51.2%
| Is This Answer Correct ? | 108 Yes | 8 No |
Post New Answer View All Answers
Explain the working principle of Synchronous Generator and Assynchronous generator?
what is formula for calculate thermal overload in new numiricalrelay( not in bimetal relay)?
The windings of a transformer are divided into several coils, because?
why can we use cosine wave instead of sine in ac supply as both have same rms vale and ripple factor
How To Convert Apparent Into Real Power Without Knowing Reactive Power?
What is the method for testing the differential protection stabilty in generator? When the time of starting What will happen if differentail protection connection wrong means?
which mm cable should be used for 1.hp immersible pump motor for the distance of 330 metres?
What are the site acceptance tests for power cables, DG Sets, LT panels & 30kVA UPS ?
If UG power cable both ends are to be earthed or what? If not why?
can i use ups power as a raw power for another ups
What is the formula for calculating impedance of transformers connected parallel at fault level 50KA?
For a stable system, where should the poles of a system be in a root loci plot?
how to calculate compresor capacity?
Define the overload capacity of the motor?
hi i will D.E.E.E.is completed pls send rrb diploma old qustion papaer sent in my e mail. i.d.