Answer Posted / suresh
VFD – variable frequency drive..
VFD is useful in energy saving because it reduces the
motor speed as demand decreases.When the speed is reduced
the power consumption Will also reduce because ,
Power = (speed)3 {cube of speed}
For example if the speed is reduced to 80% of the maximum
value the power consumed will be reduced by 50%
Power consumed = (0.8)3 = 0.512 = 51.2%
Is This Answer Correct ? | 108 Yes | 8 No |
Post New Answer View All Answers
Why dry type cast resin transformers tap link blast in HV side while power shut down times on load?
How to calculate Temp from Resister from PT100 equation,
what is the advantage of connecting capacitors in delta than in star?
What is T’Q and X’Q and X’D ? and what is saturated as well as unsaturated ?
given data are load current & power factor cable core size? plz any one update the calculation formula
63MVA,220KV/6.9KV Transformer LV side neutral is connected to Earth pit through NGR. Whether this earth pit required to connect with near by below grouding earth mat or it is to be kept separate?
Usually in the L & T make MCC feeders' power circuit,we have BMR after the MAIN CONTACTOR.,can we interchange their position, keeping the control logic same???
what is the chiller and working principal
How to select transmission line type (i.e. 11kv or 33kv) for new established industries
state basic meaning of 'INDUSTIAL AUTOMATION'?
is this the formula of building wiring to get the main breaker.Watts/volts*.8%+higher motor*(25%)=ampere. yes or no or send the correct formula for building wiring.
why we used ZNO in Lightning arrester.
Write down the brushes of a de machine.
1.ZEBRA conductor(large size) 2.KUNDHA conductor( small size ) 3.panther conductor(very small ) 4.lepard conductor (very very small)
Which motor will you choose which can operate in both lagging as well as leading power factors?