How to conduct Magnetic Balance Test, Measurement of
Excitation Current (both on HV- and LV-side) and vector
group on a 1000 KVA distribution transformer. There is a
neutral on HV side.
for magnetic balance test apply the 415 v volt to R phase
then measure Y phase voltage it must be 60 to 80 % of i/p
voltage and B phase should measure around 40 to 20 % of i/p
volatge and when voltage applied to Y phase R & B phase
should read 40 to 60 % of i/p reading. For voltage applied
to B pahse reading should be reverse of first case.
and for measuring excitaation current just give 415 V to
either side H.V or L.V but H.V side prefer and measure
current with clamp meter of all phases.
and for vector group just short the R phase of H.V with r
Phase of L.V
measure voltage as
1R-1Y =
1Y-1B =
1B-1R =
1Y-2y =
1Y-2b =
1B-2b =
1B-2y =
then e.g Dyn11
these condition to fullfill
1Y-2y = 1Y-2b
1B-2y > 1B-2b
| Is This Answer Correct ? | 7 Yes | 1 No |
Dears we deal in Chemical are Plate earthing. Kindly call if any requirement and questions. Tech Earth Solutions Mohit Verma 8791071007
which electrical supply used for long distance traction 1.1-ph 22kv a.c 50hz 2.2-ph 22kv a.c 50 hz 3.dc vtg 4.1-ph 22kv 150 jhz
Which of the following plant has less plant factor ? -Nuclear -Hydro -Diesel -Pumped storage
what is difference b/w bus duct & bus bar.
please anybody help me to find out the BHEL trainee Exam previous year questions papers . if u ve pls. send it to surekhared@gmail.com
How many Cylinders are there in Diesel Generator?
armature winding of dc machine produce alternating emf then it convert in to dc by using commutator.But only we consider armature resistance why don't we consider inductive reactane effect?
what is the relation between KVAR,KVA,KW?why we are mentioning capcitor rating in kvar?what is meant by arcing horn and horn gap in transformer?what is equipotential wire?
Formula to calculate fault current flowing in the neutral line?
what happen if the load connected to the induction motor is taken away? the same question for synchoronous generator in synch i think that the the exitation voltage will appear on the terminal only if so plz answer me
WHY DO VOLTAGE TRANSFORMERS FAIL DURING EARTH FAULT IN THE DELTA CONNECTED 6.6KV ELECTRICAL SYSTEM
How to perform a DC resistance test In Alternator and their proceduces?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)