pt range is -45 psi to 45 psi.friends can you give answer with calculation and with linerity scale like 0%,25%,50%,75%& 100%?
0 % = (-45) PSI = 4 mA
25%= (-22.5) PSI= 8 mA
50%= 0 PSI = 12 mA
75%=22.5 PSI = 16 mA
100% 45 PSI = 20 mA
Calculation :
LRV = (-45) PSI
URV = 45 PSI
SPAN = URV - LRV = 45-(-45) = 90
Calculate % of SPAN for e.g. 0 PSI is {(0-(-45))/SPAN}*100 = (45/90)*100 = 50% of SPAN
mA= [{(% of SPAN)/100}*16]+4 or in other terms ...
1% of SPAN = 4+0.16 = 4.16 mA
2% of SPAN = 4+0.32 = 4.32 mA
3% of SPAN = 4+0.48 = 4.48 mA
.
.
.
.
50% of SPAN = 4 + 8 = 12 mA
.
.
.
100% of SPAN = 4 + 16 = 20 mA
Hope this will be helpful to you.
Best Regards,
Jigar Anadkat
anadkat.jigar@gmail.com
Is This Answer Correct ? | 2 Yes | 0 No |
why we are using ungrounded RTD sensor and what is difference between grounded RTD and Ungrounded?
DCS marshilling Cabinet Power supply can be replace during plant running time?
Wht is Dry Leg Calibration and Wet Leg Calibration?
what is difference between RTD and Thermocouple?
calculate the rane of level use of this values, h=3 meter density=0.9 , whats the rang?
What is the definition of direct acting valve & reverse acting valve
in my company organisation in plan to take new PLC system for replacing old relay system , for that what I/P needsd to submit to the system house of PLC supplier?
what is the analog input , analog output , digital output, digital input geven to the MSSV , CBD, IBD , START UP VENT , BOILER FEED PUMP , AOP, CEP , ETC
1 Answers Bharat Biotech, TATA,
What is a flow meter?
how u calibrate pneumatic n motorized c/v?
what does a positioner in control valve ?
why we are using MARSHALLING PANEL? what is the role?