If a capacitor bank is having rating 750kvar for 6.6kv. Then for 3.3kv how much will be the rating of capacitor bank.
Voltage is halved and also the current drawn by the capacitor bank. The rating will be 750/4 kvar
| Is This Answer Correct ? | 0 Yes | 0 No |
I have a 1000 kVA Transformer(11kV/0.415kV) and a APFC panel of 400 kVAR(LT).Now if i want to remove the LT APFC panel and install a HT(11kV) APFC panel on the HT side is the HT APFC panel will work same as the LT APFC panel(improve the power factor),if yes what will be rating of the HT APFC panel?what is the formula to calculate HT APFC panel rating???
What are the advantages of D.O.L Starter in 3 phase induction motor?
Pls say , how we calculate lux / sq.ft, which formula used for calculation
What is master trip relay? How does it work?
Is it possible to operate a synchronous 2-poles turbogenerator with a still-in-place faulted bar but electrically disconnected ???? If yes, should I act on the other phases as well ???
What is the make of breakers, transformers, generators? What are their capacities and ratings?
what is meant by Back emf ?where its occur ?
in ONAN type transformer winding temperature is lower than oil temperature at evening time but morning winding temp is higher than oil temp what is the reason?
How to calculate cable size for a particular load? i have 12 MW,11KV Motor 3 Phase, what should be cablesize? What are the points to remember for cable sizing calculations?
I have suguna 3 hp pump for my agreeculture work.It deliver the water from 45 feet well .I suffered by powercut.During powercut i got 2phase supply only .My question is can i run the pump in 2 phase supply using capacitor?.Can u explain me how to connect the capacitors?
What is the basic difference between 90% stator earth fault and 100% stator earth fault, and its phenmenona?
We have 11kV/110V three phase indoor potential transformer in 66/11kV Sub-station, where the failure of PT is frequently happening and the rating of the PT is 0.2 class accuracy, with primary star and seconday (two cores) star connected. Some experts has suggested to not to connect the PT Primary neutral to the ground because when transformer neutal NCT connection is loose; the faulty current will flow through the PT primary neutral, resulting into failure of PT. My question is: Is it necessary to remove the primary neutral connection of the PT from ground? if not, what would be the reason for failure of PT. Please guide me.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)