How to calculate VCB current rating for 2000 KVA transformer
Answer / k. kannan
Power=1.732*415*I
I =2000000/1.732*415
I=2782.5 amps
Vcb =I=2000000/1.732*11000
I=104.97 amps=I=105 A
Suitable VCB 125 AMPS
| Is This Answer Correct ? | 7 Yes | 16 No |
How to calculate cable size for a particular load? i have 12 MW,11KV Motor 3 Phase, what should be cablesize? What are the points to remember for cable sizing calculations?
In LRS how much water PH value maintain for good operation of motor?
What is the meter used to check the DG sound level.and pollution check
who invented electricity?
1. what is the meaning of bus? 2. what is the dc transformer? How it work 3.what is the function of the serge absorber? 4.How the CT and PT rating calculate/
What is differance between alternator and generator?
IF ANYONE HAVE ANY QUESTION ASK ME AT MY MAIL anmol.bhardwaj5@gmail.com
why transformer neutral and CT Secondary neutral is connected to earth?
Compare salient pole and Hndrical rotor machines.
the resstance of a thermistor is 5000 ohm at 25degreeC and coefficient is .04/degCel. A measurement with lead resitance of 10 ohm will cause an error of
WHAT SHOULD BE THE RATING OF generator required to run a pump motor of 45 Kw.
In DC while we mention the voltage we are using -48V but in case of AC we mention only 230V not -230V, why we using -48V not 48V
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)