why did the BDV test in transformer?
Answers were Sorted based on User's Feedback
Answer / suryanaik02@gmail.com
Dry and clean oil gives BDV results, better than the oil with moisture content and other conducting impurities. Minimum breakdown voltage of transformer oil or dielectric strength of transformer oil at which this oil can safely be used in transformer, is considered as 30 KV.
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / asma
No it is considered as 26kv(bdv of oil) according to high voltage engineering laboratory
Is This Answer Correct ? | 0 Yes | 0 No |
How to size a transformer which will supply power to 550kW,690V motor starting with VFD?
Working of microwave oven?
why can the rotor of 3 phase slip ring induction motor not be a 2 phase rotor?
Which oil is used in Transformer?
How to set the star delta timer setting?
what is the standard duration after failure EB power
In dc motor starter there is less voltage required for holding contactor that's may why it is called no volt coil. but in ac starter why holding contactor is called no volt coil.
what is JE exam?
2 Diesel Generators 900KVA connected to the bus bar for essential load as an alternative for power taken from 11/440V 3KVA Transformer supplying this bus bar. my question here is in the event of power failure on 11KV side can I feed the power to 11 KV bus by using the same transformer as reverse feed, what will be the inrush current???