Answer / rakesh
There will be delayed commutation , for the brushes are
still in interpolare axis , but due to the armatut=re
reaction the point of 0 flux density gets displaced in the
direction of rotation of the generator , hence the armature
coils after crossing the brushes wil still remain under the
polarities of the trailing poles , hence again a rotational
emf will be generated which again opposes the current
reversal in the commuted coil , thereby causing delayed
commutation , it is for this reason that the interpoles are
designed with the same polarites as the main oles behind it
in the direction of the rotation in case of generator , and
opposite is the case with a motor.
| Is This Answer Correct ? | 2 Yes | 0 No |
What is the technical reason for adopting color coding of three phase system as RYB.
if two transformers are parallel & both have fault short ckt. impedance of 50KA in each case will it increase or decrease show example?
can any one tell me the formula to select the thickness of wire selection according to ampere rating
What is grid collapse? what is the reason for it?
what will happen if ac and dc supplies given
How to find Cable size? Caterpillar generator produce (Two generators) 127*2=254 amp at 11 kv . What would be the cable size (XLPE) to supply 256 amp at 11 kv? Air or surrounding Temperature is 32 degree C. Cable will go under ground at 2.5 feet depth. Group Rating Factors is 3 cables. Clearance between cables is 7 cm. Soil Temperature (Ambient) 28o C Soil Thermal Resistivity is 1.2 K.m/W I would like to use 3 separate single core instead of using 3 core cable. Some says I should use three separate single core 120RM cables. Some says 70RM .some says 95. I m totally confused. Is there ant specific rule to determine cable size? What would be the LT cable size to flow 500 Amp current? Ifte My e mail address is ifte13@yahoo.com Anyone please send me the answer to my e mail address, i will be very glad.
What is the magnetic field (coil DC ) of Turbo Expander?
How can we measure earthing resistance test (Earth meggar) of Transformer neutral pit while in live condition?.
How to check the specific gravity of the two 12 V batteries connected in series to a 24 V UPS and inverter ? will we have to disconnect all the connections and turn off the UPS and inverter or not ? will we have to check specific gravities in each cell of the two batteries ? what is the name of the instrument that is used to check the specific gravity and whats the procedure to check the specific gravity with it ? thanks
Is it possible to interlock between ACB & MCCB?
How much ph is maintained of water resistance starter for slipring induction motor ?
Dear All we are having a problem in G120 BOP showing alarm A0503, F0052, F0060 we can not remove fault alarm ,Please any body help us. kowsar
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)