Controller not working in auto mode?...what are the problem can occur...Pls explain
Question:
Controller not working in auto mode?...what are the problem can occur...Pls explain
Answer:
If a controller is not in automatic mode it is either broken or in manual mode.
In manual mode the controller's output is fixed at some percentage output and the controller is not adjusting its output to maintain the setpoint (SP).
While running at a fixed output, the process's process variable (PV) will generally stabilize at some value above or below the setpoint. PV changes will be dependent on external influences, like load changes.
However, if the output reaches an extreme, like 100% or 0%, the process can be put in jeopardy of going into a hazardous state from the uncontrolled input into the process or removal from the process of energy or mass, whatever the controller is controlling. Presumably, safeties are in place to shutdown the process should those dangerous conditions result from manual mode.
Carl Ellis
Measure First
Is This Answer Correct ? | 4 Yes | 0 No |
In dcs contol valve parameters showing like this Gain=1 or 2 , ti=7 sec, td=20sec. But temp,pressure,level control valves we are using in which type parameter side using ti,td clearly tell me
difference between repeatability and reproductability
State four different types of flow measurement, for gas flow measurement MMSCFD is the common unit expand the unit and specify significance of word S in the unit.
how 3 out of 2 Logic/interlocks works? give brief explanation with help of diagram.
what do you mean by Loop checking ? What are the cold loop check and hot loop check? what are the difference between these two loops?
what is the protection system in solar turbine compressor
EXPLAIN NETWORK COMMUNICATION ON DCS?
what r all the closed loop used in boiler? for this related tell some web address..
Lube oil pressure transmitter local it's showing 9.8 kg/cm2 but dcs side it's showing 9.26 like that what is the reason?
capillary type tranmitter using remote seals and capillary tubes filled with liquid of known of known density so if you wanna callibrate it just close block valve just before capilary @ high side & connect druck apply it's calibrated range pressure as normal calibration ensure low side block valve must be closed & if you asking commissioning so this is not a DP type pressure tx so simple if you wanna put in servie this tx just open high side block valve & than low side block same way i do it but still transmitter showing -13 ma.just tell me what i want to do ?
what is the principal of flow transmeter,level trans meter,presser transmeter?
what is gas metering system? gas chromatograph? and gas compressors?