is dc transformer is possible ?
Answers were Sorted based on User's Feedback
Answer / rakesh gupta
No, A dc transformer is not possible. A transformer secondary coil generates voltage(induced) when there is a variation of flux though its coil which is produced by pulsating current in the primary coil which is not possible with dc source. however a dc voltage regulation can be possible with dc to dc converter.
Is This Answer Correct ? | 11 Yes | 0 No |
Answer / sauvik biswas
Chopper is often said to be dc transformer
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / pavali.sreenivasulu
not possible because of transformer winding will be damage
Is This Answer Correct ? | 1 Yes | 4 No |
if a 3phase 100kva distribution transformer , 400 v,50 hz, 4-wire system is loaded at 160 k.w mostly 1-phase Lighting & Airconditioning split a.c load what will be the net effect on the power system in terms of voltage, powerfactor, current , efficiency of xformer
the rating of fuse wire i always expressed in what?
can we install LT panel & HT panel in one room?
Difference between PLC and SCADA ? What are merits & De-merits of PLCs ? What are merits & De-merits of SCADAs ?
( Re: WHAT SHOULD BE THE RATING OF MCCB FOR 415V,3Ph,50KVAR CAPACITOR BANK Answer # 1 The capacitor current would be kvar x 1000 / (415 x sqrt3). This would be 70a approx. The MCCB selected should have *atleast 1.4 times this current i.e. 1.4 x 70= 98. So you should choose at least 100 A mccb.) regarding to this answer,i would like to know why the current have to times 1.4 to get the right amphere for the mccb.hows the formula to get the 1.4??tq
HOW TO DO GRID EARTHING IN INDUSTRIES FOR A PRODUCTION BUILDING
Up to how much limit of HP of electric motor the Star- Delta Starter can be used ?
Does the direction of rotation of d.c. Shunt motor would get reversed if the armature current and field current both are reversed?
how to decide the load on secondary of the tranformer
transformer 3 ph, 225 kva pri 480v, sec 208v. primary neutral connected to system, is secondary neutral to be grounded and how
What is meant by line losses, how do you prevent the losses?
at the time of starting back emf of a motor is zero.so how can it will start to run??