transmitter in 3 connection +,-,And test mode so how Use To Test Mode
The 'test' connections on a 2 wire, loop powered pressure transmitter have a diode behind them.
If a milliampmeter is connected across the test terminals (in parallel with the diode), the impedance of the meter is less than the diode's, so current will flow through the milliampmeter. There is not enough voltage drop to forward bias the diode and the diode will not conduct with a low impedance meter circuit connected across it. The diode turns off and the current flows through the meter.
Test terminals are provided for loop troubleshooting so that loop current can be measured without breaking or opening the loop circuit so that the milliampmeter can be put in series in the loop circuit.
Carl Ellis
Measure First
Is This Answer Correct ? | 13 Yes | 0 No |
Isometric drawings are generated during _________________ phase of a project
hiii.... can any one provide me previous years question paper of hindustan petroleum for instrumentation engineering???
As you are fresher in Instrumentation & control engineer.Then why should I select you?
In case of Transmitter's(e.g.Ultrasonic Flow meter ) we have an normal practise of selction of upstream and downstream distance such as (20D and 5D ).can anyone please let me know whow to calculate "D" ?? i guess it refers to pipe thickness is t right ?
what are the difference between conventional and smart transmitter.
What is Fieldbus?
In control valve , Failure position : Close If it is Fail close(FC) during failure of AIR.. what will be the initial/ normal position of control valve is it normally open or close? please some one explain soon..
What are the advantages and benefits of using PLCs to automate a section of a plant?
what is the PC interface and software for connection to ABB logic module “ LM011-CE18RAC “ ( for Programming ) ??
In separator VFD frequently trip with OVER VOLTAGE Fault What is the reason?
what is orifice plate? Give me best answer?....plz
What is output of Thermocouple at 25 deg c