phase association of 3PH L&T static CT meter is wrong.
means 1PH & 1 CT connected properly and other 2 voltage and
CT's inter changed. what would be the impact in the reading?
Answers were Sorted based on User's Feedback
Answer / manjunath tc
Phase angle error will come into picture and meter will record slow.
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / shankar
Lets us understand this problem by taking load as constant and the incoming supply initially it was RYB in sequence.
let Vr=10<0 Ir=5<-10
Vb=10<-120 Ib=10<-20
Vc=10<-240 Ic=15<-10
Now the total power is P=VrIrcos(-10)+VyIycos(-140)+VbIbcos(-250).
=41.5 watts.
Now lets us consider Y and B phases were wrongly connected to each other
Vr=10<0 Ir=5<-10
Vy=10<-240 Iy=10<-20
Vb=10<-120 Ib=15<-10
Now the total power is P=VrIrcos(-10)+VyIycos(-240)+VbIbcos(-130).
=3.781 watts
so the energy meter will records less units
Is This Answer Correct ? | 2 Yes | 2 No |
Answer / surendar
if 415 v is appliex at three phase in your situationi f r phase is right it will get
higher vol. and other two get lower vol....right ans should be all the three
sholud b same
Is This Answer Correct ? | 2 Yes | 4 No |
we want low electricity at lower speed of fan.what we have to do?
if a 3 point starter is not available, how can a dc motor be started?
3 Answers Accenture, BIT, Techno Solutions,
Hello Can I use step up HV transformer 440/4160V as a step down? Thanks Evgeny
what will happen when power factor is leading in distribution of power?
10 Answers AMET, JTO, Power Grid,
How much DC or AC Current that a Human Body withstand for Electrical Shocks?
I need bhel previous year quetion papers for electrical engineering department.I searched but i could not find out
1 KVAR = 1.3Amps but, 25KVAR capacitor/690V capacitor takes just 21Amps as leading current, what is the reason? Please explain...
1.what is difference between line,neutral and earth 2.IF single phase voltage is 230v ac and what should be the voltage between line to neutral,neutral to earth and earth to line
How to do maint. Of busbar.
what type of earthing is done on hilly rocks.
for 24000kv transformer what is the value earthing resistence?
What is resistance reading of earth copper rod with grid and without grid?