phase association of 3PH L&T static CT meter is wrong.
means 1PH & 1 CT connected properly and other 2 voltage and
CT's inter changed. what would be the impact in the reading?
Answers were Sorted based on User's Feedback
Answer / manjunath tc
Phase angle error will come into picture and meter will record slow.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / shankar
Lets us understand this problem by taking load as constant and the incoming supply initially it was RYB in sequence.
let Vr=10<0 Ir=5<-10
Vb=10<-120 Ib=10<-20
Vc=10<-240 Ic=15<-10
Now the total power is P=VrIrcos(-10)+VyIycos(-140)+VbIbcos(-250).
=41.5 watts.
Now lets us consider Y and B phases were wrongly connected to each other
Vr=10<0 Ir=5<-10
Vy=10<-240 Iy=10<-20
Vb=10<-120 Ib=15<-10
Now the total power is P=VrIrcos(-10)+VyIycos(-240)+VbIbcos(-130).
=3.781 watts
so the energy meter will records less units
| Is This Answer Correct ? | 2 Yes | 3 No |
Answer / surendar
if 415 v is appliex at three phase in your situationi f r phase is right it will get
higher vol. and other two get lower vol....right ans should be all the three
sholud b same
| Is This Answer Correct ? | 2 Yes | 4 No |
What is the meaning of dsl line in eot crane , and why it is Called down shop lead ? Pls tell exact answer.
What is the formula to find maximum load of a DG (Single phase and Three phase)?
hi friends can u tell me name of the sites where i can get animation of electrical machines......
Why cannot we insulate HT over head cable to avoid ionization of air around the HT Cable?..By this we can minimise corona loss also..
1.what is the difference between transformer differential and busbar differential.2)why we are using 2 slope for trafo diif and 1 slope for busbar diff.3)what is the purpose of metrosil and stabilizing resistor in high impedance relay circuit.4)how metrosil reduce the peak volage.5)what is the funtion of stabilizing resistor
A 15 kw squirrel cage motor having a maximum efficiency of 90% on a continuous full load has temperature rise of 42 degrees celcius after 30 min and 52 degrees celcius after 1 hr under the above operation conditions. a) calculate its final steady state temperature rise on continuous load and the heating time constatnt. b) if the motor is operated on a short load for 9 min estimate its temperature rise. c) calculate the maximum overload that can be applied on a short, 9 min rating so that the temperature rise is the same as the final steady state temperature rise on continuous load.
what is advantage of using star to delta in place of dol starter
what will happen if frequency is below 50 hz?
How you will determine the volume of oil in a particular Distribution transformer.
What is the rating of a circuit breaker needed for 300 kv load in 33KV supply line of 33/415 transformer ? Whether 800/1200 amp vaccum circuit breaker can perform for a 33 KV line in input in 415 volt in output of the transformer ?
how can calculation ate Amps for cabel. Ex-for 1sqmm wire hou many amps we can draw
how we can classify the circuit braker???????
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)