what will happen if secondary of potential transformer
(220kv/110volt) of any metering core or protection core
(cables) of any phase got earthed??
As the secondary voltage is only 63.5 V wrt ground ,nothing
happens if the contact is with the dry earth . If there is
any dip in voltage or blowing out of fuse under other
conditions , energy meter may record less and the distance
relay may act in the protection scheme with directional
relay becoming non-directional
Is This Answer Correct ? | 0 Yes | 0 No |
What is a advantage of Self Reset Lockout ? On Fault breaker get trip & fault no longer exist then self reset lockout how inform us?
what will happen if multimeter(selector switch at DC voltage) and terminal at current is connected to DC supply?
what is the purpose of using filters in a protective relaying scheme?
Why High voltage are generate noise ?
How to covert the ac to dc and how to control the dc output?
how to calculate EXCITATION VOLTAGE & CURRENT in ALTERNATOR
What is the purpose of starter and choke in tube light?
9 Answers Chimay Brewery, TATA, TSPL,
can you explain the rms value in simple words....
what is the problem occer in motor
some practicle study shows that the reactive power at the receiving end is not equal to the reactive power at the sending end.But according to theory the reactive power is exchanged by different parts of the network – capacitors and reactors permanently, but is never consumed or produced. Then Where that reacrtive power loss occuring?is there any formula to calculate reactive power loss?
in magnetic field we send current to generate flux,why not voltage?
In power plants the reading changes abruptly to give value (MW -25) (MVAR -15) What are the reasons for this? What is the solution?