what is the ka rating of mccb.
and how it is decided .
Answers were Sorted based on User's Feedback
Answer / aditya shirbavikar
The rating of any circuit breaker is decided on the basis of its breaking capacity. so, the KA rating of MCCB is the unsymmetrical breaking capacity for a particular time.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / s.lenin
The KA Rating of MCCB is Defined as maximum current flowing
through the conductor or with standing capacity of the
breaker.the KA is decided mostly that incoming transformer
fault current
| Is This Answer Correct ? | 1 Yes | 0 No |
The value of the kA rating determines how much current the circuit breaker can withstand under fault conditions. The circuit breaker only has to withstand this for a brief period of time, usually the time it takes for the circuit breaker to trip. For example, a value of 6kA means that the circuit breaker can withstand 6,000 amps of current during the brief time it takes to trip.
| Is This Answer Correct ? | 1 Yes | 0 No |
Testing procedure of DG alternator stability test
why the generator operating along with the infinte bus bar should never be under_excited?
can we replace Dyn11 transformer to Yy0 transformer and what is the difference between the two type
why ht line fuse wire is so thin
What are the tests to be done on circuit breaker?
In a Tap changing transformer where is the tap connected , is it connected in the primary side or it is connected in secondary side
Why the cost of CT increases with the decreasing of its CT Ratio (Technical Reason)?
i am using auto transformer for starting of induction motor to provide reduse voltages...but the principle of a tansformer according to definition"which transform energy to on circuit to another circuit with constant power and constant frequency". so if i am using reduse voltage then current obsely hige because power is same.but we use auto transfarmer for starting of induction motor to give low current.but here according to definition we are giving hige current.
In ACS 1000 drive we are using 12 pulse converter,why don't use 3 pulse converter.
How to calculate KW saving for power factor correction from 0.92 to 0.98 at 350KW load?
Can you explain about TEE protection scheme?
why we use separate earthing for two seprate machine??
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)