Can we used Condensate Pot on flow transmitter which is
using on liquid having sluge and DP transmitter is in pit
and below the process line,Can we used Condensate pot for
accamulate the Sluge?
Answer / carl_ellis
Yes, you can use a condensate pot to accumulate the sludge.
It's just a version of a "drip leg" that extends down
vertically below the tap or port for the impulse line (at
the datum elevation) to the DP transmitter. Other methods
are just constructing a drip leg from pipe fittings that are
rated for the temperature and pressure.
A consideration is whether the drip leg or pot can be
drained to remove the sludge, because it will fill up over time.
Carl Ellis
Measure First
| Is This Answer Correct ? | 3 Yes | 1 No |
1)unmovable objects have frequency or not?if that object have frequency,how do we measure and transmit? 2)how do u measure the continuity without multimeter? 3)we put 24volt dc supply in railway track how many distance it is traveled without voltage drop?
yogokowa field bus system transmitter all's we are geting IOP fault in Contiunes please help me fine how we can normal the broblems?
what are different types of cables used in instrumention how to calibrate a level transmitter online ( rosemount )
Type of level transmitter commnly used in Procees area are the following. a.________________This type of level transmitter works as follows
What is minimum distance between three thermocouples (2oo3) mounted on same pipe line (20")? Technically accepted by stright line mounted or circler mounted?
So I'm a first year apprentice and I'm having a tough time with knowing the difference between AI, AO, DI, DO. I'm having a hard time understanding what devices are which and why. Can someone explain this to me?
what is the imbustion control loop
Distributed control system
Which products are available in the Mass Systemswitch and System Manager AC range?
what is the deference bitween DCS and PLC SCADA HMI System for Power Process Industry.
If we increase PI controller what will be action.
Consider a control valve action,the inlet air pressure is only 6 ksc but physically how it can be operate against 100 ksc line fluid pressure?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)