if There is Short circuit in Power Transformer, what will
happened to Buchholz Relay.??
How Buchholz Relay will respond.??
Answers were Sorted based on User's Feedback
Answer / venkatesh
it will sense the fault and gives trip command...because it is used for oil temperature protection
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / lalit lohmorh
Buchholz relay also known as gas actuated relay when fault
occured in power transformer gas actuated and BR sense the
fault and gives trip command to panel system relay which
trip the O/G breaker to transfomer
| Is This Answer Correct ? | 1 Yes | 0 No |
WHAT IS DIFFRENCES DCS & PLC
What is electrical charger?
how to check the LRS resistance .......................
how to select proper cable for ct wiring so that drop within the limit.
what is bausbar?
What are the properties of a resistor?
What are the advantages and disadvantes of delta and star connections in transformers and alternators?
How to calculate load requirement of a 50 flat apartment with 5 kw each unit,sizing of cable,transformer
what is meant by magnetic flow meter ? explain its working principle ?
effect of decrease in excitation?
how much amps can i connect for 4core 120mm armade cable
Why neutral is used in electrical system?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)