Answer / satorp
For a general installation connected to DCS, reading at DCS
will overanged > 100%. If there is Barrier installed it
will limit energy to field therefore no potential for
ignition spark at SC area.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / carl_ellis
Part I.
Let's assume the question involves a 2 wire, loop powered
transmitter powered by a 24Vdc power supply in series with
the transmitter and a load resistor across the analog input
of the receiver device.
The loop current is nominally 4-20mA.
The power supply negative is wired to the analog input
negative.
The short puts a positive 24Vdc on the (+) side of the
analog input.
The load resistor for the analog input is across the (+)
and (-) terminals, so the resistor now 'sees' 24Vdc across
its 250 ohms.
Part II. extra credit. Calculate the wattage spec needed
for a 250 ohm resistor to survive the short circuit in the
2 wire, loop powered cable.
Carl Ellis
Measure First
| Is This Answer Correct ? | 4 Yes | 2 No |
1.what is controller proportional gain 2.what is the controller intergral action time. 3.A proportional plus derivative controller that has a proportional band of 20% and a derivative action time of 0.1 minutes. Construct the shape of the output waveform for the triangular input if the input rises and falls at the rate of 4 units per minute.
Someone Please tell me what are the Pre-Commissioning activities in a Thermal Power Plant for an instrumentaion Engg.
Why Pressure Transmitter is NOT installed before up-stream of an ORIFICE PLATE? in a flow measurement.
why generation of syncronized generator increases when frequency of grid is less then 50Hz & generation decreases when grid frequency goes up from 50 Hz, as comparision with set value entered in govering panel?
What is the difference between mmwc and mmwg?
tell me the temp range of rtd?
To calculate temperature, why we multiply 25 with mV?
why use MMWC unit
i have used level transmitter in starch cooking preparation tank. tank total height 2mtr.sometime LT display shows some error value when tank is fully empty and diaphragm side i already checked okay no problem in diaphragm area. field cable checked 24volt and mA shows correct value while tank empty mA is 4mA. 4mA i needed that 0% but display showing 10% or 15% percentage values are varying continously please give any good solution for me.....
what is an ambient temperature?
Calibration procedure for electro magnetic flow meter
diff bw range and span?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)