Good Evening all.My question is - For a feed water line to
an equipment if i need to measure the flow we will use
orifice /magnetic/vortex depend on cost/spec.If i need to
measure a ''Alarm''signal and ''Interlock'' from one point
i think we can use orifice type in one location with 2
different tapping points - one for alarm and one for an
interlock to flow valve..If in case i need to have both
these signals(Alarm & interlock) from magnetic flow
meter,is it possible??will 2 seperate sensors will be
located inbuilt r we can program it ??..i thk we can have
one transmitter with these 2 signals...need to know any
technical issues are there?pls clarify
Answers were Sorted based on User's Feedback
Answer / carl_ellis
If this is not SIS (safety instrumented), the 4-20mA from a
single flow transmitter can feed a separate I/O modules (4-
20in, relay out) an alarm module and a separate interlock
module.
Or, depending on the converter/transmitter model, most
magmeters have at least one assignable relay output, some
have two relay outputs.
I've always used orifice flange unions that have only one
set of taps. There might be a double tap flange unions, or
I suppose you can drill and weld the pipe for taps. But
again, unless this is SIS, why would you? Decisions made
on a 4-20mA flow signal on a PLC?DCS/Controller/I?O modules
can do multiple functions.
If your situation is SIS, you should state that.
Carl Ellis
Measure First
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / carl_ellis
It seems you are using a flow meter's relay(s) to generate
alarm signals at various amplitudes: low, low/low, hi,
hi/hi.
The flow meter doesn't really use these alarm signals
itself, rather it generates the alarm signals and provides
the alarm signals to other devices, for whatever purpose,
alarm, annunciation or an interlock.
There might be a flow meter with 3 alarm relays. I don't
know. That's a shopping issue.
Most places will use a PLC, a controller or a DCS to
generate alarms from the analog flow signal.
But if your flowmeter doesn't have enough relays, then use
a "DC alarm trip" I/O module with the flow meter's 4-20mA
analog output.
The modules have an analog input and one or two relay
outputs with adjustable setpoints. There's probably a
dozen models on this page:
http://www.api-usa.com/signalconditioners_alarms.php
These I/O modules are not used "in a magmeter", they're
external I/O modules.
They place a small burden resistance in the 4-20mA circuit,
need an enclosure and AC or DC power to operate, but they
accomplish the task of providing multiple alarms at various
setpoints.
The 4-20mA signal is wired in series with the I/O module
and any other receiver devices.
Carl Ellis
Measure First
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / thiagaraj
@CARL ELLIS.. Thanks for your response.In case of using
Alarm (or) Interlock it was a normal practise that we
use ''LOW''LOWLOW'' (OR) ''HIGH''HIGHHIGH'' signal in the
same instrument(orifice etc)..If i need to
use ''LOW''HIGH''LOWLOW'' in the same Instrument is it
possible to use these 3 alarms in a single instrument(flow
transmitter )..If yes is it can be used in Magnetic flow
meter ..pls state its advantages and disadv also.pls clarify
| Is This Answer Correct ? | 0 Yes | 1 No |
what happens when the profibus fails while in operation (operation of a valve)?
Anybody know how to create a ladder programme for power switch in TV remote without using counter... ie TV can be turn on and turn off using single push button switch... on pressing the switch first time TV turn on and hold the on state till i press the switch again, and after TV turn off.
sir i m preparing for BARC but i am not getting any papers to prepare for this exam so please send me some sample papers to my i.d for the preparation of barc.
Can please tell mi about SIOS, PRM, SERVER, and what is the diference between PIN LAN, PCS LAN,APC Server, and please send the Doc if possible for referance,mail id patil_amit17@yahoo.com
Why Flow measure in Square-root?
How can corrosion alter the accuracy and precision of a C- Bourdon tube pressure gauge?
Foe selecting control valve if i have the min,normal & max data of flow rate,inlet pressure& outlet pressure,inlet tem.&density than how can i assure that these data are correct,pl. let me know if therew there is any method to check it.& also how we assure that the Cv we get from this data is suitable for valve for controlling require flow.
What is require for PLC Programming?
how to check control valve was passing?how to check online?
Why does a pressure gauge installed on reactor, doesn't have any vent line below to release the pressure? Is it any kind of designing mistake or it actually does not require any vent line? And if it does not require any vent line below it then how we are gonna release the pressure built inside the pressure gauge?
0 Answers Process Control Technologies,
any body please send me the old question papers of ongc test.
How earthing can be checked????
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)