Good Evening all.My question is - For a feed water line to
an equipment if i need to measure the flow we will use
orifice /magnetic/vortex depend on cost/spec.If i need to
measure a ''Alarm''signal and ''Interlock'' from one point
i think we can use orifice type in one location with 2
different tapping points - one for alarm and one for an
interlock to flow valve..If in case i need to have both
these signals(Alarm & interlock) from magnetic flow
meter,is it possible??will 2 seperate sensors will be
located inbuilt r we can program it ??..i thk we can have
one transmitter with these 2 signals...need to know any
technical issues are there?pls clarify
Answers were Sorted based on User's Feedback
Answer / carl_ellis
If this is not SIS (safety instrumented), the 4-20mA from a
single flow transmitter can feed a separate I/O modules (4-
20in, relay out) an alarm module and a separate interlock
module.
Or, depending on the converter/transmitter model, most
magmeters have at least one assignable relay output, some
have two relay outputs.
I've always used orifice flange unions that have only one
set of taps. There might be a double tap flange unions, or
I suppose you can drill and weld the pipe for taps. But
again, unless this is SIS, why would you? Decisions made
on a 4-20mA flow signal on a PLC?DCS/Controller/I?O modules
can do multiple functions.
If your situation is SIS, you should state that.
Carl Ellis
Measure First
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / carl_ellis
It seems you are using a flow meter's relay(s) to generate
alarm signals at various amplitudes: low, low/low, hi,
hi/hi.
The flow meter doesn't really use these alarm signals
itself, rather it generates the alarm signals and provides
the alarm signals to other devices, for whatever purpose,
alarm, annunciation or an interlock.
There might be a flow meter with 3 alarm relays. I don't
know. That's a shopping issue.
Most places will use a PLC, a controller or a DCS to
generate alarms from the analog flow signal.
But if your flowmeter doesn't have enough relays, then use
a "DC alarm trip" I/O module with the flow meter's 4-20mA
analog output.
The modules have an analog input and one or two relay
outputs with adjustable setpoints. There's probably a
dozen models on this page:
http://www.api-usa.com/signalconditioners_alarms.php
These I/O modules are not used "in a magmeter", they're
external I/O modules.
They place a small burden resistance in the 4-20mA circuit,
need an enclosure and AC or DC power to operate, but they
accomplish the task of providing multiple alarms at various
setpoints.
The 4-20mA signal is wired in series with the I/O module
and any other receiver devices.
Carl Ellis
Measure First
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / thiagaraj
@CARL ELLIS.. Thanks for your response.In case of using
Alarm (or) Interlock it was a normal practise that we
use ''LOW''LOWLOW'' (OR) ''HIGH''HIGHHIGH'' signal in the
same instrument(orifice etc)..If i need to
use ''LOW''HIGH''LOWLOW'' in the same Instrument is it
possible to use these 3 alarms in a single instrument(flow
transmitter )..If yes is it can be used in Magnetic flow
meter ..pls state its advantages and disadv also.pls clarify
| Is This Answer Correct ? | 0 Yes | 1 No |
how level can be measured in open tank with reference to pressure
Q- voltage source of 12v is driving the circuit.if circut draw the current of 0.5A them source voltage will became 11.8v.what is the power dilevered by source when circuit draw 5A current ?
how to write the program for single push button by using ladder diagram
i have height of stem drum level 1000mm.how i calculate the DP transmitter
defination of plc? why we use plc? application of plc? advantage of plc?
what is the advantage of submersible level transmitter compare to ultrasonic level transmitter?
testing of thermo-couple?
what is cascade loop and how it work and why it used instead of PID single loop? In cascade, Which loop is faster and slower? Please explain with loop drawing and example...
How to measure the dust in chimney(spm)?
how to rectify the poor signal strength in utrasonic digtial flow meter ,model:ge digital xce868i
What is smart positionar
What is diff between Ingral orifice and simple orifice?where it use?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)