yokogawa Temperature transmitter showing Error 15 which is Reverse Cal Fail (confirmation calculation result is bad) in manual they mentioned reasion That the output goes to the value set by hardware failure mode jumper. How can solve this problem ? anybody can say solution
Answer / carl_ellis
In the manual (from which you cited) the user action for
error 15 is 'contact service personnel'.
You can try that, but I suspect that it means, for all
practical purposes, replace the transmitter. I don't know
if Yoko offers a spare 'puck' that can be replaced in order
to salvage the housing and display, or not. You'll have
to ask.
You might try cycling power to it to see if an electrical
spike on the loop wiring adversely affected the processor,
and cycling the power might re-initialize it, but the
likelihood of success is very small.
When a transmitter goes to fail-safe mode, it's usually the
last act of the last performance, the actors are clasping
hands, and taking a final bow before the show closes.
tell 'em Carl sent you
Is This Answer Correct ? | 3 Yes | 0 No |
Why we are using reverse action in displacer types level transmitters on some Vessels?
What is the difference between mmwc and mmwg?
Calibration procedure for electro magnetic flow meter
What is difference between magnetic flow transmitter & Electromagnetic flow transmitter?
why do we use 4-20 ma current why cant o-20ma
What is the logic a Transmitter control a Control Valve? How the signal going to the Control valve? What are systems/Panels/cables/signal used to control valve from Transmitter?
Is there’s power on the bus (if so, state whether on the signal bus, or on a separate in the following: a) HART b) Profibus DP c) Profibus PA d) DeviceNet e) Foundation Fieldbus
Why mmwc unit is used?
what is flow and flowrate? definate and diffrentiate it? pls post a valid ans thanks in advance
in pressure gauge inside why we are using the glasarin oil?
Why is it necessary to use compensation leg to measure the liquid level in a closed or pressurized tank?
How r the calculation of process line mpm.
0 Answers Bhushan Power Steel,