yokogawa Temperature transmitter showing Error 15 which is Reverse Cal Fail (confirmation calculation result is bad) in manual they mentioned reasion That the output goes to the value set by hardware failure mode jumper. How can solve this problem ? anybody can say solution



yokogawa Temperature transmitter showing Error 15 which is Reverse Cal Fail (confirmation calculatio..

Answer / carl_ellis

In the manual (from which you cited) the user action for
error 15 is 'contact service personnel'.

You can try that, but I suspect that it means, for all
practical purposes, replace the transmitter. I don't know
if Yoko offers a spare 'puck' that can be replaced in order
to salvage the housing and display, or not. You'll have
to ask.

You might try cycling power to it to see if an electrical
spike on the loop wiring adversely affected the processor,
and cycling the power might re-initialize it, but the
likelihood of success is very small.

When a transmitter goes to fail-safe mode, it's usually the
last act of the last performance, the actors are clasping
hands, and taking a final bow before the show closes.

tell 'em Carl sent you

Is This Answer Correct ?    3 Yes 0 No

Post New Answer

More Instrumentation Interview Questions

Why DP level transmitter preferred for closed vessels and Radar level transmitter for open tanks??

2 Answers  


What is pressure,What is temperature,What is flow,What is level

4 Answers   Keltech, Petrofac,


how to change 4 wire rtd transmitter into a 3 wire rtd transmitter? as our transmitter is working for 4 wire rtd, what should do for working on 3 wire rtd transmitter

1 Answers   HHJ,


Why three wire is using with a RTD?

3 Answers   ABB, MAHINDRA,


How to do ma trim in massflow meter?

2 Answers   Pakistan Steel,


what is gas metering system? gas chromatograph? and gas compressors?

0 Answers   HPCL,


During valve sizing from all calculation you got flow coefficient CV 12,than what it means? like for selecting pressure transmitter if your MAWP is 12 bar than you select a capsule of max. 20 bar which cover your mawp 12 in same way for selecting control valve If CV is 12 than how we use it in selecting valve??????

1 Answers  


Why Differential pressure transmitter is located below the tappings points for steam & condensible vapor flow measurement application?

2 Answers  


Why boiler chimney area  oxyden sensor fixing? 

0 Answers   NTPC,


What is the difference between HMI and SCADA?

2 Answers  


how to calibrate the temprature transmitter MURCREYtype and thermocouple input type.

1 Answers   Shree Cement,


what is the relation between flow and pressure.for example relationship between level and pressure is p = phg like that i want ans for this question.and also how to calculate orifice sizing and flow transmitter. pls some one ans for this questions.

3 Answers   Orchid, SRF,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)